    Part Winding and Star Delta Motors



    Hello,

    probably i may not frame the questions in right way, as my knowledge is limited on electrical motors. but still i do my best...

    what are the different type of motors? Part Winding Motor/Star-Delta Motor/any other??

    Why different motors are used (PW/Star Delta)?

    Which one is widely used in supermarket refrigeration in europe?

    what is the difference between part winding and star delta motors?

    i am bit confused, whether connections in terminal box makes the difference in different motors (PW/Star Delta) or is it motor winding?

    Thanks



  2. #2
    Join Date
    Oct 2008
    Location
    newbury
    Posts
    1,445
    Rep Power
    37

    Re: Part Winding and Star Delta Motors

    For your homework it's best to use Google..At least you can be seen as active rather than waiting here for answers..

    Good luck.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Part Winding and Star Delta Motors

    The starting technique depends on the motor size and application.

    The most common motor is the Squirrel cage type. It can be started direct, star, delta or star\delta.
    The most common starting technique is direct connection, star or delta.

    You can find a lot of info on Danfoss web site.

  4. #4
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Part Winding and Star Delta Motors

    There are others, for single phase motors, like CSR, CSCR, and variants with voltmetric or ammetric relay.

  5. #5
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,707
    Rep Power
    45

    Re: Part Winding and Star Delta Motors

    star delta have 3 contactors to start it,part wind have 2 contactors which kick in with 0.5sec delay

  6. #6
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: Part Winding and Star Delta Motors

    Also part wind have 12 motor leads where a normal star/delta has 6

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Part Winding and Star Delta Motors

    Quote Originally Posted by Quality View Post
    Also part wind have 12 motor leads where a normal star/delta has 6
    Are you sure?

  8. #8
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: Part Winding and Star Delta Motors

    I am sure a part wind motor is simply 2 separate motor windings on the same stator usualy 50/50 but I have seen 60/40

  9. #9
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,554
    Rep Power
    24

    Re: Part Winding and Star Delta Motors

    Quote Originally Posted by Quality View Post
    I am sure a part wind motor is simply 2 separate motor windings on the same stator usualy 50/50 but I have seen 60/40
    And each motor has three leads (direct start on 50% of the winding), 6 in total

  10. #10
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: Part Winding and Star Delta Motors

    I was refering to a winding have 2 leads hence 6 per motor

  11. #11
    Join Date
    Aug 2006
    Location
    England
    Posts
    495
    Rep Power
    21

    Re: Part Winding and Star Delta Motors

    HI trane recipes used to have 12 leads because they were dual volt p/winds, copeland do a 50/50, 6 pins ,66/33, 6 pins with star point connection and newer version of 60/40 with 6 pins with double delta connection were all the winding coils are joined together which is a better winding because it generates less heat , you will find most large semi hermetic screws which are 50/50% ,6 pins have p/wind motors are double delta connection, i.e refcomps, bitzers

  12. #12
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    712
    Rep Power
    23

    Re: Part Winding and Star Delta Motors

    The Bitzer was my reference

  13. #13
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Part Winding and Star Delta Motors

    What about a closed transition star delta contactor arrangement with four contactors, elliminates the transitional spikes. Expensive so concider a soft starter with parallel line contactor.
    The transitional spikes generally kill motor windings using star delta, dependent on phase relationship cross over.

    this should wind everyone up. Its called vector shift between phases.

  14. #14
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Part Winding and Star Delta Motors

    Even with part winding you can use soft start. All you need to do is to connect the the two windings together.
    proper bridges are supplied with every part winding compressor.

  15. #15
    Join Date
    Feb 2007
    Location
    UK
    Age
    58
    Posts
    158
    Rep Power
    18

    Re: Part Winding and Star Delta Motors

    Quote Originally Posted by Magoo View Post
    What about a closed transition star delta contactor arrangement with four contactors, elliminates the transitional spikes. Expensive so concider a soft starter with parallel line contactor.
    The transitional spikes generally kill motor windings using star delta, dependent on phase relationship cross over.

    this should wind everyone up. Its called vector shift between phases.
    I certainly wish this had been incorporated into a couple of Cold Stores I worked on in the past - would have saved many motor rewinds - managers get a very glazed look in their eyes when you mention vector shift.

  16. #16
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    157
    Rep Power
    16

    Re: Part Winding and Star Delta Motors

    Was the same on a mixer I took over, it had, amongst it's many faults, been wired delta-star. Replaced the whole lot of control gear ( aside from a timer) with a soft starter, added a lot better interlock to it and enclosed it in a sealed cabinet. Stopped the minor issue of the mountings pulling loose from the floor every so often, and I was able to replace the supply breaker with a saner rated one. Adjusted the soft starter to give it's longest run up time, made for a smooth start irrespective of load.

  17. #17
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Part Winding and Star Delta Motors

    1) part winding 60:40 or 66:33 motors are used in european supermarkets for compressor motors above 7.5 kw . these motors can be started up without the use of compressor unloading mechanism ... example a start unloader like suction discharge by pass line .
    2) 66:33 motors are better than 50:50 as these can take start up loads better . First 66% winding is switched on and within one second the balance 33% winding comes on via timer . This sort of start up also helps restrict the start current kick since only one winding ( part winding ) is put across the power . Both can be interlocked , that means if one winding trips , both windings should switch off to avoid motor operating on part winding .
    3) Caution : do not switch on smaller part winding first . INDIVIDUAL WINDINGS NEED INDEPEDENT OVERLOAD RELAYS OF DISCREET RATING
    4) Star delta motors start with 30% of power whereby compressors must be switched on with 100% unloaded start .