    Post Commissioning issue walk in freezer!!



    Problem: Cold room not reaching temp lowest -15. But with product in it -8

    Condenser operating on r404a orifice 2
    Sight Glass full, Suction has slight frost back 6 inch from compressor
    Evap
    Air on: -15
    Air Off:-19.9
    Back Pressure: 1.1bar (-30temp)
    Suction Line temp: -8
    Condenser
    Air on: +18
    Air Off: +35
    Head Pressure:225-250psi (+38)
    Discharge Line temp: +60

    What am I missing!!!!!



  2. #2
    Join Date
    May 2005
    Location
    london
    Age
    59
    Posts
    29
    Rep Power
    0

    Re: Commissioning issue walk in freezer!!

    it might sound stupid, but have you checked whether the defrost heaters are on.....happened to me once

    was that suction line temp taken at the evap or a remote condenser ?

  3. #3
    Join Date
    Mar 2006
    Location
    belfast
    Posts
    239
    Rep Power
    19

    Re: Commissioning issue walk in freezer!!

    Close the door lol

  4. #4
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: Commissioning issue walk in freezer!!

    Fans are going the right way and coil is free of ice? New room pannels used so insulation is not a problem? Snow buildup around evaporator fans?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Commissioning issue walk in freezer!!

    Have you checked the evaporator superheat, did you install MOP TXV

  6. #6
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Commissioning issue walk in freezer!!

    Suction pressure to low, head pressure to high. Suction SH to high.
    I would suggest incorrect TEV SH setting to high or orifice size is to small (lowing the suction), and maybe a slight overcharge (increasing discharge).
    One other point, has this room been designed for storage only or product pull down (-8C product)

  7. #7
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: Commissioning issue walk in freezer!!

    Cheers for the posts.. I am sure it has been designed for pull down but I will have to double check we actually lowered the suction pressure as this was the only way we could achieve it to drop bellow -10 the condenser is operating on fan speed also but going with an ambient of +18 head pressure seems ok. Im looking more to wards the orifice size because everything else seems to be doing its job. We had the evap super heat set for 6k and it would not pull down bellow -10 it was left for hours.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Commissioning issue walk in freezer!!

    Quote Originally Posted by COBRAKAI View Post
    We had the evap super heat set for 6k and it would not pull down bellow -10 it was left for hours.
    Are you saying there was 6K superheat at the coil outlet and you adjusted it higher? If so, there's your problem.
    Last edited by Gary; 17-07-2011 at 10:24 PM.

  9. #9
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: Commissioning issue walk in freezer!!

    Cobrakai

    How did you lower the suction pressure? ("we actually lowered the suction pressure as this was the only way we could achieve it to drop bellow -10 the condenser")
    What are the room dimensions and duties of the condensing unit/evaporator?
    Where did you measure the suction line temperature?

    Alec
    Mostly found in the southern part of this green and pleasant land.

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Commissioning issue walk in freezer!!

    The evaporator is being starved of liquid

  11. #11
    Join Date
    Mar 2011
    Location
    SCOTLAND
    Posts
    29
    Rep Power
    0

    Re: Commissioning issue walk in freezer!!

    Cheers for the posts again lads..
    Went back to site and de-gassed system blew the lines out with ofn and checked over expansion valve. Issued triple vac and re commissioned. System took a few hours but eventually T1 reached -20. T2 Evap temp -26. Was thinking there may have been a blockage or an issue with expansion valve. evap superheat was 9k any more was causing floodback any less would not achieve sufficient temp. subcooling was 8k was wondering if this was ok for a pipe length of 5m? Personally I still feel the system may be undersized due to the volume of people entering the freezer it is a very busy restaurant hence the long time for pull down. product is stable at -18 though. I will post all information including system installed and commissioning data to see what what yous think. Maybe yous could help me adjust it for better efficiency.. In the mean time just got a call out.. Sigh!!!!!