    is this check valid for non condensables



    I am checking for non condensables in R22 balanced pressure on both guages is 8.9 Bar
    @23C on the PT chart this corresponds to R22, I then put gauges on a bottle of reclaimed 22 at the same ambient and the gauges read 9 and a bit bar, can I now assume hat there are no NC's present, the PT's were taken at the compresser service valves which has been idle for 24 hours the ambient at the comp was 21.9C
    Devlin



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: is this check valid for non condensables

    Hi devlin
    The above method is not acceptable for checking non condensables. Your reference is reclaimed refrigerant which could have non condensables or contaminants in it. Also the ambient temp is constantly changing.
    The way to check it is to either pump down or reclaim the system refrigerant, measure accurately the temperature of the refrigerant and the pressure of the refrigerant then compare with a PT chart.

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: is this check valid for non condensables

    Tesla Virgin R22 is not available over here any more ! Only reclaimed or recycled .
    Devlin ideally you need to recover a couple of kgs to a clean cylinder and check using a PT chart
    Cheers
    Stu
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  4. #4
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: is this check valid for non condensables

    Thanks guys just to clarify, the cylinder of 22 I have is newly purchased recycled 22 that I got to top up this system, and, it is this I used as a base line and refered to the R22 PT chart, the figures there obtained were compared to the system charge pressure as read from the gauges and as in my original query, the results from the bottle of "new" R22
    and those from the system gauges are as close to identical as you can get so in conclusion system PT and Bottle PT are the same wouls that then not indicate a NC free system
    Dev

  5. #5
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: is this check valid for non condensables

    Devlin, i would have thought that standing pressure and temperature could only give guidance to "type" of refrigerant. Non condensibles, depending on percentage of refrigerant charge, will hang around the highest point of the system doing nothing untill refrigerant is circulating, then causing havoc to system pressures.. Mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  6. #6
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: is this check valid for non condensables

    My understanding is that in a balanced system IE standing idle with high and low sides at equal pressure and at a given ambient and a known refrigerant, R22 in this case, any NC's present will alter this PT regardless of where the NC's are hiding as they will affect absolute pressure due to the fact of their prescence and the more knowledgeable of chemistry can in fact tell what those NC's are although that may be speculative, my reasoning is if a bottle of "clean" R22 gives the same results as the system in the same location and ambient then there is no NC's present,
    Devlin
    PS found this which would indicate I am on the right track 2nd page
    http://www.refrigerants.com/pdf/NRInews-Smr11.pdf
    Last edited by devlin maguire; 15-07-2011 at 09:35 AM. Reason: another thought and some stuff from NR

  7. #7
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    Mar 2007
    Location
    england
    Posts
    394
    Rep Power
    18

    Re: is this check valid for non condensables

    Dev unless you can be sure that the temp of all the major refrigerant holding components are the same(ish) your results are a guess at best especially if there is no saturated vapor present, as a gas will take a sensible heat gain with no significant rise in pressure.

    Best practice is to pump down into the condenser and leave the fan running on the condenser until you can be confident that the refrigerant is at ambient temp.
    Quidvis Recte Factum Quamvis Humile Praeclarum.

    Latine dictum, sit altum videtur.

    Si hoc comprehendere potes, gratias age magistro Latinae.

  8. #8
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: is this check valid for non condensables

    Hi devlin
    It clearly states to isolate refrigerant in the condenser (unless I read page 2 wrongly) which would indicate that you are incorrect. Please reread your reference on page 2 and point out where it states your method is accepted or admit you have misinterpreted this information. The ambient temperature is constantly changing and the temperature of the refrigerant in a container could be different to the temperature of refrigerant in a condenser.
    At the end of the day the only way to do the test is with accurate measurement of the refrigerant temperature and accurate measurement of the pressure of the refrigerant isolated in the condenser or where the whole charge has been reclaimed into a container. There must also be liquid refrigerant present. These values are then compared to a PT chart and where a few PSI difference is measured there are non condensables present in the system.

  9. #9
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: is this check valid for non condensables

    Hi guys, fair point(s) I may have mis read or interpretated it wrongly, although I still maintain that if I have identical figures for both system and known NC free samples at the same ambient same location then that wouls indicate a NC free system,However I will today extract 4 Kilo of gas from the system and recheck, it is not feasable to pump down the system or run fans mainley due to time constraints today, thanks for your input it is very much appreciated
    PS would'nt the sight glass indicate moisture ?
    Dev