    AHU offcoil temperature



    Hi all, wondering is there a formula to calculate desired offcoil temperature if we want a room temperature of 24 degrees celsius.



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: AHU offcoil temperature

    Sorry, there isn't, even not a rule of thumb. I should say, the warmer the better.
    Q= m.c.DT
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: AHU offcoil temperature

    Quote Originally Posted by wankidal View Post
    Hi all, wondering is there a formula to calculate desired offcoil temperature if we want a room temperature of 24 degrees celsius.
    You need to ensure that the air off temperature is low enough to ensure good enthalpy exchange in the room. I would suggest at least 6K below the room required condition

  4. #4
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    639
    Rep Power
    20

    Re: AHU offcoil temperature

    You need to go back to basic psychometrics and plot the process on a psych chart.

  5. #5
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: AHU offcoil temperature

    Another one...again,...,coming here once with a question reading some answers and then disappears, even without a simple 'Thanks'
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  6. #6
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    714
    Rep Power
    19

    Re: AHU offcoil temperature

    Quote Originally Posted by Peter_1 View Post
    Another one...again,...,coming here once with a question reading some answers and then disappears, even without a simple 'Thanks'
    part of the job spend the day on a roof in the pissing down rain then off you go without a kiss my arse or a thank you

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: AHU offcoil temperature

    The coil air off temp needs to be 11K lower than the room temp in order to achieve 50% RH.

  8. #8
    Join Date
    Jul 2011
    Location
    Singapore
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: AHU offcoil temperature

    ok thanks a lot peeps. sorry was busy and left this site unattended. well i guess should put more time into this forum. hope that we can discuss more topics here

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: AHU offcoil temperature

    If we plot our target room conditions (24C@50%RH) on a psychrometric chart, this gives us a target dewpoint of about 13C (11K below room temp).

    Keep in mind that moisture can only be removed if the coil surface temp is below the air dewpoint temp.

    As the air moves through the coil, moisture drops out, reducing the dewpoint of that air, until it's dewpoint matches the coil surface temp. At this point, no more moisture will be removed, because the surface temp is no longer below dewpoint.

    In point of fact, due primarily to coil bypass factor, the coil air off temp is somewhat higher than the coil surface temp, but this difference generally compensates for normal latent loads. Going by air off temps puts us in the ballpark for most applications... and air off temp 11K below room temp is a viable rule of thumb.

    After a few days of operation, we may want to check the actual room conditions and adjust accordingly. If the actual dewpoint is running 1 degree above target, we might want to lower the air off temp 1 degree. If the actual dewpoint is running 1 degree below target, we might want to raise the air off temp 1 degree... etc.

  10. #10
    Join Date
    Jul 2011
    Location
    Singapore
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: AHU offcoil temperature

    I am still trying to understand your post. Kinda lagging in certain technical terms. Its been ages since i read my acmv textbook. thanks a lot anyway

  11. #11
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: AHU offcoil temperature

    .

    Gary says 11K and I have no problem with that.

    I was always told to work to a rule of 10.

    Air off is 10 degs lower than air on.
    Evap temp is 10 degs lower than air off.

    This is a rule of thumb that works for me, but it is not the only answer and
    the application will alter the correct amounts.

    A rule of 10 is a good start point and then take it from there.

    taz

    .