    Smile BRC1C62 compatible with BRC1B52/52 ERROR codes E5 and J1



    HI Guys,


    Please don't be too harsh as this is my first post and I'm not actually a refrigeration engineer. I'd just like some advice to pass onto my air con repairer. In Australia Daikin are quite restrictive with their sharing of info and my local fridgie in country SA hasn't beeen able to provide the info. HE is really great with Panasonic!!

    My air con is Indoor Unit FDY60FV1A Outdoor Unit RY60EV1A
    with a BRC 1B52/62 controller. The controller is a bit worse for wear as the case is the worse for wear. I can source a BRC 1c62 for $40. Will this be compatible?

    The unit reports a E5 - outdoor activation of overheat protection which will not reset and also a J1 - Malfunction of pressure sensor.

    The unit works really well when cooling and takes up to 15 mins to defrost outside unit in cool weather.

    ANy advice that you can provide re these two errors would be great to pass onto my local fridgie.

    Thanks for your help and take care.

    Hill



  2. #2
    Join Date
    Nov 2008
    Location
    australia
    Posts
    136
    Rep Power
    16

    Re: BRC1C62 compatible with BRC1B52/52 ERROR codes E5 and J1

    hey mate, I know daikin can be a bit tricky hope this helps your fridgey.
    Diagnosis 39
    5.2.3 OL Activation (Compressor Overload)
    Remote
    Controller
    Display
    E5
    Method of
    Malfunction
    Detection
    A compressor overload is detected through compressor
    OL.
    Malfunction
    Decision
    Conditions
    �� If the compressor OL is activated twice, the system
    will be shut down.
    �� The error counter will reset itself if this or any other
    error does not occur during the following 60-minute
    compressor running time (total time).
    * The operating temperature condition is not specified.
    Supposed
    Causes
    �� Refrigerant shortage
    �� Four way valve malfunctioning
    �� Outdoor unit PCB defective
    �� Water mixed in the local piping
    �� Electronic expansion valve defective
    �� Stop valve defective
    Also check the discharge thermistor.

  3. #3
    hill's Avatar
    hill Guest

    Re: BRC1C62 compatible with BRC1B52/52 ERROR codes E5 and J1

    HI Cool_Tech,

    Thanks for your speedy reply and apologies for my late thanks. I must have somehow missed your reply.

    Will pass info on. Unit still working well but still seems to take up to 15 mins to defrost outside unit when temp drops behow 5 degrees centigrade

    Thanks again

    Hill

  4. #4
    Join Date
    Aug 2011
    Location
    england
    Posts
    29
    Rep Power
    0

    Re: BRC1C62 compatible with BRC1B52/52 ERROR codes E5 and J1

    it sounds to me like it needs a service, also, if discharge thermistor is out of calibration it wont be runnng anywhere as efficeint as it should