    Re: daikin vrv's



    Stupid me - I've just caught up with the postings in the Moderators Area



  2. #52
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: daikin vrv's

    Me to, but that doesn't make me to change my post nor edit it.
    Now it comes...........again.......all the abbreviations with 4 letters, NRIJ,.....describing the whole being of a person in just 4 letters.
    A M A Z I N G
    Could refrigeration be that simple......
    Last edited by Peter_1; 24-10-2005 at 07:08 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #53
    MRcoolingMAJIC's Avatar
    MRcoolingMAJIC Guest

    Re: daikin vrv's

    Me to, but that doesn't make me to change my post nor edit it.
    Hi, Peter_1.

    What is the difference between changing a post and editing a post?

    Thanx for the attention.

  4. #54
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: daikin vrv's

    Is this place becoming all

    schitzophrenic?????????

    ( I have never been able to spell that)
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  5. #55
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Hi Raymond

    Just re-visiting this old thread.

    Did you manage to sort out the problem with your G series unit?

    Any chance of an update - don't forget - we do site visits for reasonable reward

  6. #56
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Quote Originally Posted by frank
    Hi Raymond

    Just re-visiting this old thread.

    Did you manage to sort out the problem with your G series unit?

    Any chance of an update - don't forget - we do site visits for reasonable reward

    Hi Frank,

    First things first, ever thought of moving to Cambridge. I know a company looking for a good Daikin engineer, Unfortunatly they got me instead

    Strangly got called back to the site today as the customer wants it SORTED OH REALLY !!!

    Now, can't be arsed to go through previous posts to see what i've put plus my dial up is getting slower and slower so would take me all night, what i think however

    VRV has a cooling rating of 162.5
    Indoor units add up to 212 so in theory should have never worked. Customer response "It used to work !"

    Now the reception area of the building used to be seperate rooms but now its all gone open plan so i think more duty is being put on the unit. Also the unit is getting older (Arnt we all) and therefore probably having to work harder.

    Now, i would like to reclaim, vac out overnight and regas. My problem then is, If i regas to the original VRV spec, surely this is enough gas to cope with a 162.5 capacity and not 212, therefore how much extra gas should i put in.

    The problem its on a fully comp contract. Therefore my company doesn't want me to spend vast amounts on gas and it not clear the fault, the customer on the other hand doesn't care how often they call us as i doesn't cost them.

    Oh the joys of the job

    Regards

    Ray
    Last edited by Latte; 11-01-2006 at 07:51 PM.

  7. #57
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Raymond

    First things first, ever thought of moving to Cambridge. I know a company looking for a good Daikin engineer, Unfortunatly they got me instead
    What's the PAY like

    My daughter lives in St Ives so I'm a regular visitor to the area

    Customer response "It used to work !"
    Yes but did it work as it should?

    Now, i would like to reclaim, vac out overnight and regas. My problem then is, If i regas to the original VRV spec, surely this is enough gas to cope with a 162.5 capacity and not 212, therefore how much extra gas should i put in.
    You just can't overcharge a system that is out of manufacturers spec and expect the extra refrigerant to make it work It is out of design - full stop (based on your previous information). What you need to do now is come up with a solution to make the system work - not to just give the customer what he wants to hear.

    Why not suggest to the customer that you ought to bring in a Daikin specialist to confirm the system is not installed to manufacturers specs and that to solve the problem will cost him some money? after all it's not your fault. Plus I may get to spend the night visiting the daughter

    I'll only charge the same as Space Air or Daikin UK

  8. #58
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Quote Originally Posted by frank
    Raymond


    What's the PAY like

    My daughter lives in St Ives so I'm a regular visitor to the area
    Hi Frank,

    Better speak to cooling-gurus about that one

    Looking at the site list i have, the main reception open plan area just off it have 2x40's 1x32 & 2x25. This if my math is righ is 162. There are two other units on this system on offices both 25's. I suppose the obvious answer would be to take these two off the circuit and put on their own condensing units.

    Sounds simple but i expect it to be a pig of a job.

    Anyway i have done my bit, i can only report what i find. Its up to those far higher up the ladder than me to come up with a solution

    Regards

    Raymond

  9. #59
    Join Date
    Aug 2004
    Location
    England
    Age
    51
    Posts
    744
    Rep Power
    25

    Re: daikin vrv's

    Quote Originally Posted by rdocwra

    VRV has a cooling rating of 162.5
    Indoor units add up to 212 so in theory should have never worked.
    I don't know too much about these things but...
    Can you not size a vrv/vrf at 130% ? because not all indoor units will be switched on or running at 100% all of the time.

    ie 162.5 +30% = 211 therfore,just inside the design limit.

    cheers

    eggs

  10. #60
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    There are two other units on this system on offices both 25's. I suppose the obvious answer would be to take these two off the circuit and put on their own condensing units.
    Unfortunately you can't put VRV indoor units on normal condensing units. Each VRV indoor unit has a built in EEV for refrigerant control and Skyair condensing units have the EEV on the outdoor.

    Although you could use the 2 x 25's on a super multi but this would be more expensive than just putting in 2 new split systems.

  11. #61
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by frank
    Unfortunately you can't put VRV indoor units on normal condensing units. Each VRV indoor unit has a built in EEV for refrigerant control and Skyair condensing units have the EEV on the outdoor.

    Although you could use the 2 x 25's on a super multi but this would be more expensive than just putting in 2 new split systems.

    this is a R22 system so you're effed anyway...

    cheers

    richard

  12. #62
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Quote Originally Posted by eggs
    I don't know too much about these things but...
    Can you not size a vrv/vrf at 130% ? because not all indoor units will be switched on or running at 100% all of the time.

    ie 162.5 +30% = 211 therfore,just inside the design limit.

    cheers

    eggs
    Not quite Eggs.

    In one respect the system can operate at 135% capacity which will mean that the indoor performance is reduced but the maximum index of the outdoor unit should not be exceeded. The high end index number relates to the 135% capacity so if you go over this then the indoor performance reduces even more as is evident by Raymond's system.

    When designing a system you should calculate the indoor index numbers then select the outdoor to match - if some of your indoor units only run very little and you don't mind the temporary drop in performance then you can select the outdoor at a high index.

    It's easier to understand with the selection charts in front of you

  13. #63
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Eggs,

    I theory it could work like that, unfortunatly since they have gone all open plan the units are having to work hard all the time, especially as the receptionist thinks she's in spain and runs it at 25 all day long. I think the system would have coped before as units will have shut down in their smaller area's but no chance of that now

    Regards

    Fatboy

  14. #64
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Raymond

    I found this troubleshooting guide for checking refrigerant charge
    Attached Files Attached Files

  15. #65
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: daikin vrv's

    Nice one, thanks Frank
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #66
    Join Date
    Dec 2005
    Location
    Johor
    Age
    62
    Posts
    151
    Rep Power
    19

    Re: daikin vrv's

    RD
    I was going to mail message you some details regarding the fault encounter but system was down. Here are the attachment. Mine are all hardcopies, hard to post the manuals down here. If you're here maybe I can hand it over to you.
    Hope this things helps.
    Attached Images Attached Images

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Daikin VRV Checker
    By bobjob in forum Air Conditioning
    Replies: 6
    Last Post: 04-01-2009, 08:10 PM
  2. New to RE and needing Daikin Help
    By Owen in forum Air Conditioning
    Replies: 20
    Last Post: 25-09-2008, 06:55 PM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •