    daikin vrv's



    Hi Frank,

    Got a problem with a VRV that keeps going out on E4 (LP Switch).

    Other engineers have check the switch and it isnt going out. After suggestions from Daikin the compressor and the discharge line sensor have been replaced. Is there anything else on the system that could cause an E4 fault

    Regards

    Fatboy



  2. #2
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: daikin vrv's

    Quote Originally Posted by rdocwra
    Hi Frank,


    After suggestions from Daikin the compressor and the discharge line sensor have been replaced.

    How can a system with a dead pot trip an LP switch?

    .
    ________
    Lincoln Continental Mark IV
    Last edited by Argus; 07-02-2011 at 08:38 AM.

  3. #3
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Guys,

    I wrote the original post while i was in the office before going out to the job just in case someone had come across this before.

    Today, was the first time i had been to this site for this problem, apparently this problem has been going on for months with sucessive engineers failing to find the fault.

    The VRV is a RSXY5GY1 and it runs 7 indoor ceiling systems on 4 controllers (One controller does 4 units the other 3 have seperate controllers). All the controllers show E4 fault. In the past engineers have fitted equipment onto the LP switch to see if thats playing up but no good. I think the pot was changed in case that was throwing a wobbly.

    Now today, i have reset all the controllers and run them on test mode and all OK. Check gas 10bar discharge and 4.4bar back pressure (Seems high for R22) fans indoor and outdoor all ok and suction frosting back to pot. All units set to 23 degree C on cool mode. Checked LP switch wiring and all OK.

    The problem in the past i am told is the unit works fine for a couple of weeks and then throws his code up for no apparent reason

    Any Ideas anyone

    Regards

    Fatboy

  4. #4
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Question Re: daikin vrv's

    I may be wrong!!! but best guess is that if all 7 units are running and you have 10 bar hp then system is short of refrigerant. 10 bar 150psi approx. is low for r22. 4.4 bar 65 psi approx seems ok. when the temp decreases and units begin to shut down on thermostat {4 on one control and 3 single} the suction will drop {possible lp fault}. as far as my knowledge of daikin goes the inverter will slow down and after that a hot gas unloader will open {rsx10h} have you tried running just one ahu to see what happens. i have {more than once} come accross a daikin unit where the "self diagnostic" fault code bears no relation whatsoever the system fault. good hunting.

  5. #5
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Guys,

    Thanks for the replies, The only thing that concerns me is that the VRV is already frosting back to the compressor. Surely if i put more gas in then this is going to get worse ?

    Regards

    Fatboy

  6. #6
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    I have to say, that I do not have many experiences with G-series, this is quite vintage model, but...
    First of all, the LP switch should be tripped under 2bar.
    If you were there and it tripped over this pressure, the switch is wrong. But it won“t be your case I guess because of frozen suction pipe.
    Second thing you should check is the low pressure sensor. Unfortunately, I do not know what pressure sensor is really there. Check the supply voltage 5VDC between black and red. The output voltage (If there are 4 wires - between black-green or white, one is not connected, if there are three wires between black and white):
    Low pressure = (Outp. volt - 0,5)*10/3
    Check with gauge manifold.
    Then, if this is OK, check the subcooling at test mode, if there is no subcooling, there could be refrigerant shortage, but if there is some subcool, refrigerant shortage is not your problem.

  7. #7
    Dns's Avatar
    Dns Guest

    Re: daikin vrv's

    Yes, agree with martind. If the above is OK. the you have to replace the outdoor PC card.

  8. #8
    Join Date
    Sep 2005
    Location
    uk
    Age
    53
    Posts
    499
    Rep Power
    21

    Re: daikin vrv's

    Firstly i am assuming all 7 units are calling for cooling so th cond. unit is fully loaded, are the coils and filters clean. heavy suction frosting sounds like poor evaporation in any situation but you state that all machines are set for 23c so this {in theory} should not happen. the only true way to determine your charge is to recover and weigh back in. i know this sound like a real ballache {and unnecessary if you know what your doing in the first place} but i did this on an rsx10 and found 6kg short much to my disbelief. system charge must be added to calculated extra for pipework and ahu's. this will eliminate any doubt over gas related problem. all the info on this should be in the original daikin installation book if they have it. i still wouldn't rule out circuit boards. in short "it could be ****ing anything!".
    Last edited by slingblade; 10-10-2005 at 03:59 PM.
    Takes a licking, keeps on ticking.

  9. #9
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: daikin vrv's

    Code E4 blinks for 'G' series either low pressure switch set value out of calibration.
    Low pressure switch activates due to shortage of refrigerant or clogged piping.
    Defective Outdoor PCB. or pressure sensor defective.
    With a high pressure of 150psig for R-22 will be consider under charge.What is your ambient outdoor air temperature?
    But with a suction pressure of 65 psig definitely you can't get any frost on the suction line, 65 psig for R-22 is above freezing point of water.
    I think there are more to check on the system, either you may have an erratic pressure gauge.

  10. #10
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Guys,

    Ambient about 18 degree C, Pressures via Manifold gauges as no gauges on unit so should be correct to within a couple of PSI.
    Diffinatly frosting back to the compressor.

    Looks like someone needs to spend some time there and climb into the roof and check over the indoor units.

    As usual didn't have too much time on site, Oh the life of a Refrigeration Engineer is such a busy one

    Regards

    Fatboy

  11. #11
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    That is the best work. No time, customer standing behind you, and mysterious problem. Tomorrow I have to go for something like this. I really like my job sometimes :c
    Just make checks of the LP switch and sensor. The compressor frequency is controlled according to LP = 5-6 dg. C. If the low pressure is wrong measured, then the frequency could be higher >> system goes to low pressure.
    If the LP sensor is OK, you have to check temperatures after all indoor units, as you already mentioned and the liquid temperature.
    Good luck

  12. #12
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: daikin vrv's

    Quote Originally Posted by rdocwra
    Hi Guys,

    Ambient about 18 degree C, Pressures via Manifold gauges as no gauges on unit so should be correct to within a couple of PSI.
    Diffinatly frosting back to the compressor.

    Looks like someone needs to spend some time there and climb into the roof and check over the indoor units.

    As usual didn't have too much time on site, Oh the life of a Refrigeration Engineer is such a busy one

    Regards

    Fatboy
    What kind of indoor air temperature do you have?
    18 degrees outdoor will never turn 'ON' the compressor with a thermostat setting of 23 degree.
    Unless you have a very high heat load found in the air-con room.

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Hi Raymond

    Sorry for the delay in responding but today is the first day back after a well earned break in the SUNSHINE

    Over the years, I have learned that whatever the Daikin fault code says is 99.9% true. Computer logic only has one path.

    If you are getting an E4 fault then you have a low pressure system malfunction.
    This could be caused by a number of things,
    Failure of low pressure switch
    lps wiring is broken or faulty
    failure of lps connection to pcb
    loss of refrigerant charge
    failure of outdoor pcb
    cause related to system as a whole (their words not mine )
    malfunction of refrigerant piping circuit

    Now, without a crystal ball or site visit (chargeable at reasonable rates ) I would have to look at the symptoms step by step:
    1) system runs and fault occurs randomly so no loss of refrigerant
    2) system runs for 2 weeks (as per previous post) so it is an intermittant fault - could be faulty wiring, pcb fault, lps fault etc.
    to check the switch and wiring it would be safe to link out the connection to the pcb for a couple of weeks as it seems the gas charge is OK.
    If the system runs Ok with the switch bypassed then it would not indicate a fault with the pcb or refrigerant circuit

    And you mention that the system frosts back to the compressor. I would look toward the circuit piping (is it within maximum distances?, any kinks in the pipework?, does the compressor ramp up and down excessivly?, are the indoor units within the index allowed? etc.
    It is very difficult to pinpoint the fault from a distance but you must use logic.
    Can you post a list of the indoor model numbers? with this I can determine the index rating

    I have a piece of kit that connects to the pcb and tells me what every part of the machine is doing at any particular time on the laptop - very useful in these situations
    Last edited by frank; 12-10-2005 at 08:58 PM.

  14. #14
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Frank,

    I will pass that on to my boss (Cooling-gurus) and let him sort out what our next step is.

    I will send you a PM as i need to ask about things but not on the forum

    Regards

    Fatboy

  15. #15
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Frank,

    Just good the unit details from the file in the office

    According to our records the outdoor is a RSXY5GY1 and it feeds 4 x FXYS25G's 2 x FXY40G's and one FXY32G. all the indoors are on the ground floor. I dont think the pipe run is excessive it certainly shorter than some i have seen. What is the maximum pipe run on these units.

    Another question slightly related. When a unit comes precharged for a 15 meter pipe run i assume this is in total (suction and discharge meaning indoor and outdoor unit must be no more than 7.5 meters apart) is this correct or is it 15m on each suction and discharge

    Regards

    Fatboy

  16. #16
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Hi Raymond
    I'll look up the Daikin details tommorrow at the office and post back. The maximum indoor outdoor distance for a G series VRV is 100m (loosely the same for most makes in the early days - pre R407c/R410A) with the first indoor unit to last indoor unit being 40m. So you could go 60m of pipe from the outdoor unit, then make your first indoor unit and then feed all the other units making sure that the they all fall within the 100m limit.

    It increased to 125m for R407C, with the first indoor unit a maximum 75m from outdoor.

    When the manufacturers state a maximum pipework distance it refers to a one way measurement so if it's charged for 15m sepeation then it can be 15m - not divided by liquid and suction lengths.

  17. #17
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    to MrCoolingMagic:
    This is good example E0
    From my experiences E0 is common malfunction, if the indoor unit needs cooling and the outdoor does not cool from any reason, which could not be detected by any other protection.
    E0 is descripted as an activation of protection device (fan thermal protection and overcurrent relay), but...
    Some of E0 cases:
    Instanteneous power failure - in many many cases
    Inverter problem - totally burnt or some disconnection
    Reversed phases (in case of older small Split units)
    Outdoor PCB cold junction on some connector
    Mechanically blocked compressor
    etc...

  18. #18
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: daikin vrv's

    Quote Originally Posted by bladesling
    llllllllllllllllllllllllllllllllllooooooooooooooooooooooolllllllllllllllllllllllllllllll
    lmfao daikin really are ****e. s.h.i.t.e
    Sounds like you've got a bit of an axe to grind with Daikin.

    Care to elaborate.

  19. #19
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    Man, this is the thread for your effusions.

  20. #20
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Quote Originally Posted by bladesling
    LOL how much did that red herring cost?
    Whatever the cost it is worth it to keep our customers happy .

    This is one of those jobs that you have to be in the right place at the right time. If anyone can sort these out it's normally Frank. Bladesling, i am surprised you have had many problems wih Daikin. Mostly they are more reliable than some other makes i could mention.

    Regards

    Fatboy

  21. #21
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by rdocwra
    Whatever the cost it is worth it to keep our customers happy .

    This is one of those jobs that you have to be in the right place at the right time. If anyone can sort these out it's normally Frank. Bladesling, i am surprised you have had many problems wih Daikin. Mostly they are more reliable than some other makes i could mention.

    Regards

    Fatboy
    he's a salesman who judging by some of his posts is suffering from quite a major inferiority complex both personally and the kit he has to sell....

    still the way he's going about it he won't be here long .

    cheers

    richard

  22. #22
    Join Date
    Sep 2005
    Location
    england
    Age
    61
    Posts
    17
    Rep Power
    0

    Re: daikin vrv's

    I have been following this thread with some interest
    i like most have had dealings with daikin direct and through their agents some of which no longer exist
    i have had warranty issues on replacement compressors which have been faulty at start up,when original compressor has run for years {different faults i might add) where daikin will not replace unles a serial no is given, and when you tell them it is nolonger readable they just shhoo you. i have experience of an agency selling warm climate heat pumps to a user in the uk (45 splits in total}so that in winter they do not operate in heating etc etc

    i believe daikin are called daikin as ford already had the name anglia

    my apologies to frank as throughout all my grief he has been of great help in sorting out all the c**p that generally ensues when you are called to a daikin installation
    :eek:Why on earth would somebody do that?:(

  23. #23
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by fridge51
    I have been following this thread with some interest
    i like most have had dealings with daikin direct and through their agents some of which no longer exist
    i have had warranty issues on replacement compressors which have been faulty at start up,when original compressor has run for years {different faults i might add) where daikin will not replace unles a serial no is given, and when you tell them it is nolonger readable they just shhoo you. i have experience of an agency selling warm climate heat pumps to a user in the uk (45 splits in total}so that in winter they do not operate in heating etc etc

    i believe daikin are called daikin as ford already had the name anglia

    my apologies to frank as throughout all my grief he has been of great help in sorting out all the c**p that generally ensues when you are called to a daikin installation
    As mentioned our Daikin warranty % is currently at naught. I agree we are not immune from technical problems but if you employ competent good quality guy's and work to a decent standard then Daikin will seldom if ever give problems.


    Pretty much all the manufacturers know that most warranty calls are usually install related and if you are always having troubles on daikin sites then I suspect someone is giving away a lot more information about themselves that you'd prefer customers not to know..

    A friend who was a warrenty tech for Mitsi (now operations manager for LG) would always always check to wiring first on any call he went on and usually this was the 'problem' not the kit

    A lot of monkeys have got into this game over the last 5 years and it shows..

    cheers

    richard

  24. #24
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by bladesling
    still the way he's going about it he won't be here long .



    Agreed. the INTERNET fridge police are most likely on the way as i type.

    This is the best forum for discussing refrigeration /air conditioning I know and it's kept that way be stopping ijits and trolls from abusing it.

    Alt.hvac was the best but look at it now..competely ruined by bad language and trolls spoiling it.

    Look at fridgeman-something tells me you know this site... ruined by the mod allowing all sorts of stuff to go on so the serious guy's with information leave (and usually come here saying "what a breath of fresh air it is")

    The only way for this site to continue it's good work is to stop this stuff.Others have been banned here for less than what you've posted thus far so don't feel persecuted BTW

    Have a think about it and either join in and give us the benefit of your experience or go to either of the above mentioned and post there..



    cheers

    Richard

  25. #25
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    As mentioned our Daikin warranty % is currently at naught. I agree we are not immune from technical problems but if you employ competent good quality guy's and work to a decent standard then Daikin will seldom if ever give problems.
    Well said Richard. That's my general feeling, but, I also have had issues with Daikin, although, through SpaceAir, I've never had any real issues that haven't been sorted.

    One such problem was No.6 compressor failing on a VRV install. (26hp outdoor with 9 indoors rated at 52kw cooling.) Seems that the crankcase heater was incorrectly sized during design stage so that, when the last compressor was called, it just pumped all the oil out.
    Didn't take long for the comp to fail, bearing in mind that the last compressor spent most of it's time waiting for the indoor conditions to approach maximum load.
    We got paid all our costs including gas, time, expenses etc. - can't say fairer than that.

  26. #26
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Where has the fault code E0 been mentioned in this post?

  27. #27
    Join Date
    Sep 2005
    Location
    england
    Age
    61
    Posts
    17
    Rep Power
    0

    Re: daikin vrv's

    Pretty much all the manufacturers know that most warranty calls are usually install related and if you are always having troubles on daikin sites then I suspect someone is giving away a lot more information about themselves that you'd prefer customers not to know..
    i must point out that our company does not have trouble on all daikn jobs. but i find that if we attend a customer that already has an installation,that requires a service call 9 time sout of ten its a pain!

    every body must have had the 10/12 week lead time on certain spares, and before daikin uk got together suffered at the hands of cvarious agents ( you know who you are)
    as with every aspect of our industry as you rightly say, monkeys move in,unfortunately there are a lot of zoo keepers out there too

    regards to all

    phil thompson
    service director
    F T Refrigeration Ltd
    www.ftrefrigerationltd.co.uk
    :eek:Why on earth would somebody do that?:(

  28. #28
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    You are completely right gentlemen. Look at this thread. We were solving specific problem and one "reply" shifted this discussion to completely another direction.
    We cannot do anything, only ignore such replies.
    Banning users had to be done by site admin and I do not think, that he has so much time. Just be lucky, that this site exists, order must be maintained by ourselves.
    Just to turn this thread to original position:
    What is going on rdocwra? Do you have any info from your boss "guru"

  29. #29
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    OK GUYS,

    Back to the original Thread,

    I managed to get back to the site today and get some more info. Apparently this fault only occures when the unit is on heat mode .

    I have never seen a system controlled like this, although there are 4 seperate controllers in 4 different rooms in one of the rooms is a daikin panel with 2 toggle switches on it. The top one is fans to the left and temp to the right. The bottom switch, cooling left and heating right. By using this switch you lockout all the controllers into either heat or cooling mode (Does this make sense)

    Anyway thats as far as i got today. Fault in Heat mode
    Any Ideas Now

    As for Cooling-guru he get his information the same place i do (Frank)

    Regards

    Fatboy

  30. #30
    Join Date
    Sep 2005
    Location
    Slovakia
    Age
    51
    Posts
    19
    Rep Power
    0

    Re: daikin vrv's

    The control with central cool-heat changeover is normal.
    If the error is happened in heating mode you have simpler situation as you have to check temperatures only on outdoor unit.
    If I should say anything without detailed informations, in heating mode could also be the reason of low pressure the electronic expansion valve in outdoor unit. But you have to be sure, that E4 is during heating and not during defrost.
    If the error is happened only sometimes the best way to analyse this is the parameters logger. I know, that this is quite proprietary tool, but maybe you know somebody from DAIKIN who has this (the name is Daikin Service Checker). We in Slovakia are lending this to dealers if such problem occurs.

  31. #31
    cooling-gurus's Avatar
    cooling-gurus Guest

    Re: daikin vrv's

    With regard to more information for Ray, i can only give you more background on the fault, as i have had previousl engineers go to this site and carry out works as per Diakin Technical. The original complaint is the same, fault E4 occours intermittantly. Going back to the begining it all seems to start from a leak on caplillary line, which was repaired and recharged accordingly. Several calls to state the system was not working, on arrival the cutomer had reset the system and got it back working, making it difficult for us to pin point the fault. It then went out on code F3 after several checks Daikin suggested a fault with the internal valves of the compressor and the discharge pipe sensor. Unfortunately i was not convinced and went for the cheaper option of the discharge sensor. We then managed to find out that the receptionist was arriving in the morning and feeling cold tunred it on full heating then once warm tuned it down to Cooling to the original setting, this was an ongoing problem until she was told not to touch the controllers.

    Again the fault re-occoured so we opted for the compressor replacment as per daikins advice. They then suggested a Tattle Tail to be installed on the Lp switch which we did and left for some time, this did not give us any further information except it didnt blow.

    As suggested previously i think (bearing in mind i am not a A/c engineer) but as frank suggests LOGIC it must be either a PCB or Lp switch fault.

    This is based on Discussions with Ray, but what do i know------------Not alot i can tell you

    Obvioulsy changing the compressor and discharge pipe sensor on Daikins recommendations has proved that it wasn't that.

    Thanks for all the advise being given i am very appreciataive of all the help.

    Cheers

    Cooling-Guru

  32. #32
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    if the fault seems to coincide with the capillary I would look at
    a charge
    b moisture

    then go from there..

    cheers

    Richard

  33. #33
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Hi Raymond

    I've managed to look at the manual for the kit and can report the following findings

    Outdoor unit = RSXY5GY1 (Index capacity = 162.5)

    Indoor units = 4 x FXYS25G (index = 4 x 25 = 100)
    2 x FXY40G (index = 2 x 40 = 80)
    1 x FXY32 ( index = 31.25)

    Total indoor index = 211.25

    Raymond, the system is mis-matched The correct outdoor unit should be a RSXY8

  34. #34
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Thanks Guys,

    I take on Richards point about moisture, i know the system has had a gas leak in the past and the problems only started after it been repaired but need to check if its had a drier.

    Another thing, if this unit is going out on LP in Heat mode and the sytems is switchable so it can only run units in either heat only or cooling only (Not both at the same time) does this unit act the same as a split and reverse the cycle (Discharge becomes suction and vice Versa). If so if it goes out on LP is there another LP switch on the Discharge side (Suction on heat) or does the board somehow work out what mode it's in and run the LP anoher way.

    The plan is to sit down with cooling-gurus and go through the file from scratch. Maybe the first step should be reclaim all the gas, weigh it, change drier(s) and recharge. The trouble is a system of this size is going to need a long vac out (Overnight possibly - any comments)

    I knew i should of gone sick the day i first got this call

    Regards

    Fatboy
    Last edited by Latte; 20-10-2005 at 07:17 PM.

  35. #35
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    on any heatpump the suction going into the compressor is always the suction whatever mode it's running on.

    therefore if you fit the lp by the compressor it will always measure low pressure

    cheers

    richard

  36. #36
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by frank
    Hi Raymond

    I've managed to look at the manual for the kit and can report the following findings

    Outdoor unit = RSXY5GY1 (Index capacity = 162.5)

    Indoor units = 4 x FXYS25G (index = 4 x 25 = 100)
    2 x FXY40G (index = 2 x 40 = 80)
    1 x FXY32 ( index = 31.25)

    Total indoor index = 211.25

    Raymond, the system is mis-matched The correct outdoor unit should be a RSXY8
    frank what is the index of the 8 ?

    cheers

    richard

  37. #37
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    does this unit act the same as a split and reverse the cycle
    Raymond
    The answer is yes. VRV units come in three types:
    Cooling only
    Heat Pump
    Heat Recovery

    The first 2 operate exactly as a split system would (or more accurately, a multi split) the third system is what defines the VRV system. Waste heat from one room can be used in another room or rejected to atmosphere.

    A system is in balance when the heat absorbed is rejected together with the heat of compression. A VRV heat recovery system can maintain this balance under varying conditions, from fully cooling, across partialy cooling and simultanious heating to fully heating.

    One thing that must be true though is that the system operates within the boundaries set by the manufacturer. If you try to operate a VRV system outside of the published data you will get unexpected results.

    The intermittant LP fault you are experiencing is due to your system being out of balance. When the unit is operating in heating mode, all the indoor units are acting as condensers and send the liquid back to the outdoor coil which acts as the evaporator. As your system is not index balanced, the outdoor unit would be starved of liquid and would show low pressures.

    In cooling mode, the result would be low capacity on all indoor units.
    Last edited by frank; 25-05-2006 at 08:05 PM.

  38. #38
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    change drier(s)
    There is NO drier to change on a VRV
    The trouble is a system of this size is going to need a long vac out (Overnight possibly - any comments)
    The recommended time for a proper vacuum of a system is 8 hours and a triple break with OFN

  39. #39
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Richard

    The maximum index for a RSXY8 is 260, the minimum being 100

  40. #40
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: daikin vrv's

    There is NO drier to change on a VRV
    You will be surprised Frank what you can find.

    I will show you some beauties around Christmas time.

    Chemi

  41. #41
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Hi Frank,

    My guess would be that the unit would not have had an 8 hour vac or a tripple break, a couple of questions though.

    1) when would you break the vac, time,micron," of vac or just whenever.
    2) Although no drier fitted originally, would you gain anything fitting a bi-directional
    3) Even if i had a micron gauge (which i dont, not at £130 anyway) where could you fit it. Assuming you should fit it at the furthest point from the vac pump and you vac at the outdoor service ports where could you fit it. Are there any 1/4 service ports on the indoor units, ive never seen one


    Regards

    Fatboy
    Last edited by Latte; 20-10-2005 at 08:58 PM.

  42. #42
    rbartlett's Avatar
    rbartlett Guest

    Re: daikin vrv's

    Quote Originally Posted by frank
    Richard

    The maximum index for a RSXY8 is 260, the minimum being 100
    so what is max/min for the 5 then?

    cheers

    richard

  43. #43
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Quote Originally Posted by rbartlett
    so what is max/min for the 5 then?

    cheers

    richard
    RSXY5 Max 162.5 Min 62.5
    RSXY8 Max 260 Min 100
    RSXY10 Max 325 Min 125

  44. #44
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: daikin vrv's

    Frank/Richard,

    Right, Here is my thinking

    FACT:- We know the system was OK Before it had a gas leak so logic dictates tis is the first place to look

    First, go to NRS and get a Midi reclaim bottle (we think system has about 15kg R22)
    Reclaim gas and weigh, Fit Bi-directional, Tripple-vac Overnight, Regas and try.

    Anyone have objections or suggestions.

    I think i have got to start with the basics and go from there at least this way it eliminates gas. How do you charge a vrv if you dont know the pipe lenths. although this one should be within spec if the unit is underpowered or you dont know the lenghts what do you do. Pressures, Frosting back ?

    Regards

    Ray
    Last edited by Latte; 20-10-2005 at 09:28 PM.

  45. #45
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    How do you charge a vrv if you dont know the pipe lenths.
    To correctly charge a VRV/VRF you have to measure the total liquid line length and sizes. You then apply these lengths to a formula provided by the manufacturer. Do the sums and then charge the total amount.

    The problem here Raymond is that your system will not work correctly as there are too many indoor units connected to it. You have an imbalanced system.

    For Daikin (RSXY5) on R22 the formula is
    1/2" liquid line length (m) x 0.1 = ?
    3/8" liquid line length (m) x 0.05 = ?
    1/4" liquid line length (m) x 0.025 = ?

    Add all the answers up and subtract 2. Add this result to the name plate charge and the system will be correctly charged.

    However, in your case, as you have too many indoor units connected, the answer will result in an over charge.

  46. #46
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Reclaim gas and weigh, Fit Bi-directional, Tripple-vac Overnight, Regas and try.
    No objections here Fatboy but leave out the Bi-directional. No additional filter/driers are required.

  47. #47
    rbratlett's Avatar
    rbratlett Guest

    Re: daikin vrv's

    No additional filter/driers are required.
    i agree with frank, if it's not required then it's not required.

  48. #48
    Thermophysics's Avatar
    Thermophysics Guest

    Re: daikin vrv's

    i agree with frank, if it's not required then it's not required.
    You're not really agreeing with Frank, are you. You're simply stating that something not required is therefore not required by the very definition of "not required". So you're only expressing an understanding of the language rather than an agreement with the arguer. You're simply acknowledging cognitive receipt of the conditional truth.

    A more accurate expression of you perception would be "Yes, Frank, I understand".

  49. #49
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: daikin vrv's

    Quote Originally Posted by Thermophysics
    You're not really agreeing with Frank, are you. You're simply stating that something not required is therefore not required by the very definition of "not required". So you're only expressing an understanding of the language rather than an agreement with the arguer. You're simply acknowledging cognitive receipt of the conditional truth.

    A more accurate expression of you perception would be "Yes, Frank, I understand".
    What is the technical meaning of this add?

    I thought this was a refrigeration forum and not some sort of analytical psych forum where 'they' try to analyse what 'they' think you really want to say.

    Never thought at the possibility that he's just saying what he's saying/posting, nothing more, nothing less, with no other message behind the answer?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  50. #50
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: daikin vrv's

    Quote Originally Posted by Thermophysics
    You're not really agreeing with Frank, are you. You're simply stating that something not required is therefore not required by the very definition of "not required". So you're only expressing an understanding of the language rather than an agreement with the arguer. You're simply acknowledging cognitive receipt of the conditional truth.

    A more accurate expression of you perception would be "Yes, Frank, I understand".
    This sounds like a reply from Marc

Page 1 of 2 12 LastLast

Similar Threads

  1. Daikin VRV Checker
    By bobjob in forum Air Conditioning
    Replies: 6
    Last Post: 04-01-2009, 08:10 PM
  2. New to RE and needing Daikin Help
    By Owen in forum Air Conditioning
    Replies: 20
    Last Post: 25-09-2008, 06:55 PM
  3. Daikin Analyzer
    By marc5180 in forum Fundamentals
    Replies: 10
    Last Post: 02-08-2008, 07:15 PM
  4. Daikin Controllers
    By airefresco in forum Air Conditioning
    Replies: 5
    Last Post: 15-05-2008, 08:08 AM
  5. !!big Daikin Problem!! Codes,u4,pj, And E0
    By airconengineer in forum Air Conditioning
    Replies: 21
    Last Post: 31-05-2007, 09:04 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •