    Sep 2010
    denmark
    32
    8
    Discharge Temperature and Condensation Temperatures are same?
    Hello,
    I would like to know if the values of discharge temperature and condensation temperatures are same?
    Kind Regards...
    Feb 2001
    Doncaster, England
    199
    Re: Discharge Temperature and Condensation Temperatures are same?
    Morning newreflearner,
    Discharge temperature is the temperature of the refrigerant at the compressor discharge where the state of the refrigerant is superheated vapour.
    Condensing temperature is the saturation temperature of the refrigerant - in everyday language, the temperature at which the refrigerant is condensing.
    Therefore the discharge temperature will be hotter than condensing temperature.
    Hope this helps.
    Tony
    Sep 2010
    denmark
    32
    8
    Hello Tony,
    I understand..Thanks for your help.
    Good Day...
    Oct 2003
    5,630
    In some occasion,DT can be the same as CT but then there's something wrong. NI the F-gas exams, we sometimes see this where candidates don't notice that on small hermetics they have a SH of 0K where the liquid flowing into the compressor is decreasing the DT towards the CT. We can simulate this perfectly when we want it. Sometimes ,we turn before the exams start the SH screw on the TEV so that we have almost 0K and we monitor the candidate if he sees this. Or we remove the orifice completely :-)
    Mar 2009
    KZN, South Africa
    63
    2,212
    The amount of high side superheat (DT-CT) will also depend on the type of refrigerant used.
    Nov 2009
    Minsk, Belarus
    171
    Quote Originally Posted by desA View Post
    And also depends on efficient factor of compressor.
    In some places will have to think ...
    Apr 2009
    Spain
    47
    14
    And also depends on compressor suction temperature, where the fluid has collected heat through the pipe system and other elements.
    Apr 2011
    India
    94
    13
    Good replies by seniors , thanks for sharing your knowledge. I can easily understand all comments but i am unable to understand what PETER explained ?
    So, Peter i will be thankful to you if you explain it in simple words.