    could anyone tell me if an undersized peice of equipment would cause the lower half of a evaporator to freeze. thanx chaps



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: silly question

    is the gas charge right, tev ok? ur a bit vague with ur question.we need model,application,operating parameters superheat/subcooling air on/off coils,sight glass condition,age, setpoints/control strategy,-the more info the better the diagnosis-oh and piccys are useful

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: silly question

    Describe the system, temps and pressures etc.

    Would think a faulty tev, defrost heater or settings, dirty evaporator, shortage of refrigerant etc would be likely candidates too.

    Jon
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: silly question

    sounds like evap starved of refrigerant.

    - gas charge
    - expansion valve
    - poor air flow
    I've seen this bottom half freezing many times. its usually the above. but u need to provide more info.
    fridge

  5. #5
    Join Date
    Jun 2008
    Location
    gloucester
    Age
    44
    Posts
    72
    Rep Power
    16

    Re: silly question

    sorry guys will get operating details when i pop back later

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •