    Another koi pond refrigeration question



    Hi all,
    Can anyone help me with these?
    1. I need to cool 120.000 liter of water in a pond down to 22°C (initial temperature is 30°C), the pond is in enclosed area. Will 2 x 5pk compressor enough?

    2. Another one is water tank with 6.500 liter of water (3.250 liter in the tank and 3.250 liter inside the pipes), initial water temperature is 44°C and plan to keep it stable at 10°C.
    Right now they are using six unit of 2pk chiller, but couldn't bring the temperature down to the desired level, only down to 34°C. The water flow is 300 liter/minute.

    Thank you all.



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51

    Re: Another koi pond refrigeration question

    Your figures don't really make any sense. 120.000 litres = 120 litres. Do you mean 120000 litres?

    Again, does 3.250 litres mean 3250 litres?

    Can you explain what you mean by 2pk chiller and 5pk compressor?

  3. #3
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Another koi pond refrigeration question

    Well, Frank if we say 3.250 in most EU countries, then we mean 3250 and 3,250 is 3 units and 250/1000.
    I think the poster is referring to only the HP of the compressor. a 2 x 5 pk (strange he uses pk because this is the Dutch expression for hp)

    So 10 hp (2 x 5) will give you +/- 40 kW of cooling at te=0°C
    It all depends on the heat losses of the systems which are unknown and very hard to calculate. How much of the surrounding heat will warm up your water again. Is the pond covered, is the pond isolated (guess not), sun influence, wind influence, the DT between water and ambient which is never the same...

    Only a trial and error test will give you exact numbers from where you can start your calculation.

    A good reference point now is where iun the second case a DT of 10 K is apparently possible with 12 hp (6 x 2p) and you need a DT of 34K so you will need at least a total of 3.4 times 12 hp or +/- 40 hp.
    40 hp is +/- 120 kW cooling capacity.
    You have a waterflow of 300 l/minute or 18.000 l/h (18,000 for the US and UK guys :-) ), so rough calculated, your 120 kW can cool this massflow +/- 5,5°C.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  4. #4
    Join Date
    Dec 2006
    Location
    Indonesia
    Age
    74
    Posts
    37
    Rep Power
    0

    Re: Another koi pond refrigeration question

    Thanks a lot for the replies, it surely gives me something to start with.
    Sorry for the little confusion regarding the numbers, and thank you Peter_1 for clearing that up

  5. #5
    Join Date
    Jun 2011
    Location
    United States
    Age
    36
    Posts
    9
    Rep Power
    0

    Re: Another koi pond refrigeration question

    I am still a bit confused on this issue and would like someone to help me out.
    _______________________
    Search Engine Optimization
    Search Optimization

  6. #6
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,094
    Rep Power
    23

    Re: Another koi pond refrigeration question

    Hi mack