    Evaporative condenser drain traps



    Hi all
    Is it necessary to to trap evaporative condenser drain lines under all situations? The reason I ask is I have seen a couple of installations recently with no trap. I thought they all need a trap and long dropper legs to overcome the large evap/con pressure drop and to ensure a liquid seal.

    One being a single evap/con draining into a hp receiver, this system had no receiver to discharge ballance line either. The condenser has a single outlet drain line so if it was trapped it may not drain well???

    The second system is also a single evap/con draining into a hp leg with a high side float and a balance line from the leg to discharge. The evap/con has two outlets with dropers of about 500mm and then T together. This system also has a thermosyphon oil cooler connected to the hp leg.



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Evaporative condenser drain traps

    Idea of liquid trap to prevent condenser flooding.
    Example 1. No balance line. Pressure in receiver will be slightly lower and liquid will drain fine. However, liquid can flood condenser if condensing pressure drop suddenly.
    Example 2. This condenser can be partly flooded, because it has ballance line and no traps.

  3. #3
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Evaporative condenser drain traps

    Thanks Sergei, i'm glad someone replyed.
    So it would appear a trap is necessary in most situations and the main reason for the trap is to allow free draining of the liquid from the condenser.

    If no trap is installed the condenser drain line would have to be sized for sewer flow and a ballance line should be installed when the HP receiver is located where the abient temperature change is substancial?

  4. #4
    Join Date
    Jul 2008
    Location
    Houston Tx
    Posts
    42
    Rep Power
    0

    Re: Evaporative condenser drain traps

    As long as your just running 1 cond you can get away without a trap but all your piping needs to be done correctly. As for my company we add traps to all drain legs or reverse traps to headers

  5. #5
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Evaporative condenser drain traps

    Hi, Superfridge


    Quote Originally Posted by Superfridge View Post
    Hi all
    Is it necessary to to trap evaporative condenser drain lines under all situations? The reason I ask is I have seen a couple of installations recently with no trap. I thought they all need a trap and long dropper legs to overcome the large evap/con pressure drop and to ensure a liquid seal.

    One being a single evap/con draining into a hp receiver, this system had no receiver to discharge ballance line either. The condenser has a single outlet drain line so if it was trapped it may not drain well???

    The second system is also a single evap/con draining into a hp leg with a high side float and a balance line from the leg to discharge. The evap/con has two outlets with dropers of about 500mm and then T together. This system also has a thermosyphon oil cooler connected to the hp leg.
    Generally, when we have one condenser with single coil we do not need to make a trap, but one condenser with two or more coils in parallel or two or more condensers in parallel it is necessary to make a traps to balance coils, otherwise one or more coils/condensers can be out of duty ....

    .... that is very similar to home central heating system where we use balance valves at radiator outlets to balance complete system i.e. to achieve warm water circulation through each radiator ... with traps on condenser outlet drain pipes we do the same ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  6. #6
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Evaporative condenser drain traps

    Thanks for the reply Josip. You explained it well!