    Evaporator fan flow direction



    Came across an evaporator today that is the first i seen as far as the way the air flow is across the coil and wanted to make sure it was right. It is a BOHN WK075AC The question is does it matter which way the air is going across the coil ? on this evaporator the air is being pulled up thru the one fan on the bottom and blowing air from the inside out.( this makes cleaning the coil very difficult cause you can not get to the coil on the inside unless you remove the fan and blade and then you only have a 12 inch hole to work with) I would think that the air should be pulled from the outside in thru the coil and discharge thru the fan on the bottom. so i was just wondering if any of you new as to why it would be like this. Is it supposed to be like this ? what effect will it have on the system etc.....



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Evaporator fan flow direction

    Forced draught or induced draught, the evap manufacturer would have designed the refrigerant flow through coil to be counter flow to air flow for max performance. Suggest hinging the fan deck for better access.

  3. #3
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Evaporator fan flow direction

    Hi jak
    Another note on the airflow is I think it is more efficient to blow air through the coil than pull (induce) it through. this is because the air is slightly pressureised which will increase the temperature of the air slightly giving a greater temperature difference between refrigerant and air (on cooling mode). If it were heating like a heat pump it would be the opposite.

  4. #4
    Join Date
    Jul 2011
    Location
    United States of America
    Age
    59
    Posts
    86
    Rep Power
    13

    Re: Evaporator fan flow direction

    Is this evaporator mounted on the ceiling in the center of the room with a short height say 8"? If so, these are designed to be space savers so more product can be stored on shelving against the walls of the cooler or freezer. To clean, yes remove the fan guards and fan blades and start cleaning.

  5. #5
    Join Date
    Jan 2009
    Location
    Sydney
    Age
    44
    Posts
    58
    Rep Power
    16

    Re: Evaporator fan flow direction

    Tesla is right about blowing through the coil because you are taking the fan heat out of the space without cycling it around.