Thread: carrier 30gx
-
20-08-2011, 06:19 AM #1
carrier 30gx
pls help to fix this alarm in carrier 30gx chiller
alarm # 62
this alarm is coming will start up only after reseting one or two times compressor starts working normal.
-
20-08-2011, 06:43 AM #2
Re: carrier 30gx
Anish
Refer to the attached.
When did you last service your comp.
Suspect oil and or oil filter issues.
Grizzly
-
20-08-2011, 06:52 AM #3
Re: carrier 30gx
hi
we have not serviced the compressor.
we have changed 6 months before compressor oil and external oil filters.
-
20-08-2011, 06:53 AM #4
Re: carrier 30gx
Ah!
External oil filters!
What about the internal?
Grizzly
-
20-08-2011, 06:58 AM #5
Re: carrier 30gx
hi
we have not tryed that (internal oil filters)
pls advice the procedure for that.
-
20-08-2011, 06:39 PM #6
Re: carrier 30gx
Hi
you need a 19 mm alan key ,
pump down the unit ,change filter ,and back to normal operation!
good luckTHE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!
-
20-08-2011, 06:46 PM #7
Re: carrier 30gx
Sorry for not replying this morning only I was on my way out the door to work.
Anyway as Goshen suggests change the internal Oil Filter.
Follow the link below to an earlier post regarding Internal oil filters.
http://www.refrigeration-engineer.co...er+Oil+filters
Good Luck,
Grizzly
Also read the attached.Last edited by Grizzly; 20-08-2011 at 07:06 PM.
-
21-08-2011, 07:29 AM #8
Re: carrier 30gx
it is possible to pump down this unit if so how
-
21-08-2011, 07:48 AM #9
-
21-08-2011, 09:57 AM #10
Re: carrier 30gx
looks like someones after a foriegner,(work) theres not many horses in uae more camels!! oh and an arab who's stood with his finger up his a**e wondering have i pumped it down correctly -you should be able to spot him at the airport-hell have facial burns and a white stick, dont give him any passwords jesus.
-
23-08-2011, 01:16 PM #11
-
23-08-2011, 05:37 PM #12
Re: carrier 30gx
You should NOT pump down these machines, as they have a permanent live to the compressor and if a vacuum is pulled can cause the compressor to go to earth.
to change internal oil filters isolate oil valves on the oil seporator, connect a 1/4" hose to the compressor scrhrader located next to the oil solenoid and recover the oil into a suitable container there should only 50ml of oil max that comes out. then using a 19mm allen key remove the filter cap above the compressor discharge line and GENTLY remove the old filter DO NOT twist it as they can snap and if this happens it is difficult to remove.
HOWEVER this is only applicable to phase 2 and 3 machines ( black or grey prodialog control) if the unit has a HSIO controll this is a phase 1
machine in which case you will need to recover the entire charge of refrigerant then change the filter
-
24-08-2011, 06:29 AM #13
Re: carrier 30gx
hi
thank u all for ur valuable suggestions.
we ordered the filter already.
i will be back to u once its finished.
-
08-09-2011, 01:18 AM #14
Re: carrier 30gx
Off topic - needed removing
Last edited by chillerman2006; 08-09-2011 at 04:15 PM.
If the World did not Suck, We would all fall off !
-
08-09-2011, 10:18 AM #15
-
08-09-2011, 02:42 PM #16
Re: carrier 30gx
If the World did not Suck, We would all fall off !
-
12-09-2011, 08:44 AM #17
Re: carrier 30gx
hi
Replaced oil filter succesfuly and unit running good.
During the job there was some amount of gas passing from filter opening.
We Isolated all the valves and oil solid valve also.
How can this be prevented.
As we are planing to fix other units also.
-
12-09-2011, 09:57 AM #18
Re: carrier 30gx
Refer to my earlier post some units require the gas removing, please don't ask for advice if your not going to follow it!!!