    sizing evaporator to condensing unit



    Dear
    Suppose we have a condensing unit (7 tons -20F) independently of others parameters (load, humidity, distance, superheat …) what is the evaporator for this condensing unit at -20F?
    Thanks in advance



  2. #2
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: sizing evaporator to condensing unit

    You say independent: load, humidity, SH ... ARE some of the inside cold room parameters you need to calculate you evaporator. They are the determining parameters to calculate the evaporator.
    If your compressor can pump 20T at a pressure corresponding to -20°F, how big then must your evaporator be you think? The compressor is getting these 20T from somewhere, so...
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  3. #3
    Join Date
    Dec 2007
    Location
    haiti
    Posts
    26
    Rep Power
    0

    Re: sizing evaporator to condensing unit

    I think the evaporator must match the condensing unit i.e 20T at -20F also