    Hi,
    I am converting a Trane chiller from R22 to R422D. I understand the Helical Rotor compressor runs on ISO68 oil. The chiller is going to be operated at -10C. Will ISO68 be ok at this temperature or should I change it to a polyolester based oil i.e. EAL Arctic 32?
    Also, the chiller has an Adaptive Control unit on it. Where can I download a manual for this, including the password?
    Thanks
  2. #2
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    54
    Posts
    282
    Rep Power
    15
    Re: Trane Adaptive Control / Helirotor compressor - oil
    that has the machine control
  3. #3
    Join Date
    Jun 2007
    Location
    hants
    Age
    63
    Posts
    6
    Rep Power
    0
    Sparkatan ,
    You will not be able to convert to R422D. The chiller will not operate correctly with R422D and especially not at -10c.
  4. #4
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16
    Hi Paulh, thanks for that.
    The chiller currently has an operating range of +15 to -12C when operating on R22. Is there an alternative to R22 suitable for the helical rotor compressor?
  5. #5
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    140
    Rep Power
    16
    Use R407C with POE oil. I suppose that -10C is correct for RTAA. Password is ++--++ and +-+-+-
    Try to find Users manual on trane.com
  6. #6
    Join Date
    Dec 2008
    Location
    West Yorkshire
    Posts
    63
    Rep Power
    16
    Anyone have or know where I can get the R22/R404a retrofit parts list for this chiller?
  7. #7
    Join Date
    Oct 2010
    Location
    Greece
    Age
    52
    Posts
    97
    Rep Power
    14
    Hi,
    Please check your email or you can contact local TRANE sales office for selection.
    Regards,
    CV
  8. #8
    Join Date
    Jun 2007
    Location
    hants
    Age
    63
    Posts
    6
    Rep Power
    0
    Hi Sparkatan,
    The best option is to contact your Trane office. Give them the serial no and they will do a selection. The selection will be for R404a. Normally the EXV's may have to be changed out with the EXV modules as well as a good few oil changes to minimise the mineral oil content.
  9. #9
    Join Date
    May 2010
    Location
    Greece
    Age
    42
    Posts
    16
    Rep Power
    0
    contact Trane office and they will propose you a conversion kit
    e-mail me to send you the manual
    christos@firstclima.gr
  10. #10
    Join Date
    Apr 2011
    Location
    Russia
    Age
    51
    Posts
    140
    Rep Power
    16
    I am not sure you have to replace parts... Only oil.