    Flogging a dead horse.



    G'day all

    Sorry to bring up an old topic that has already been thrashed to death, but looking through archives I couldnt find an answer to my question.

    We all know that a partial restriction in a cap tube causes low suction pressure and high superheat. But so does short of gas and they can both look similar on the low side gauge when the system is running. Also an icing cappilary line could be another indication..

    What if the particular system doesnt have a name plate charge or a gauge connection on the high side so you can check subcooling to determine whether there is a partial restriction.?

    Does taking the temperature in the mid point of the condenser coil give you a proper indication of SCT good enough to do a subcool measurement?

    I wonder how many mechanics stuff cap tube systems full of refrigerant until the suction line gets colder thinking they are short when it is actually a restriction.

    Does anyone know of a foolproof method that will enable you to get it right first time without trying to hunt down a non existant leak.

    Thanks in advance.



  2. #2
    Join Date
    Aug 2005
    Location
    Australia
    Age
    42
    Posts
    44
    Rep Power
    0

    Re: Flogging a dead horse.

    Something that has always plagued me as well temprite, would be keen to see what sort of replies come back,

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Flogging a dead horse.

    Hi guys,

    Cap tube can and is tricky at times. You have to trust your experience when charging these systems.

    Most cap tube systems, operate above 0C° so its easy to see when the frost clears at the end of it.

    you have to pay attention to pressures, both suction and discharge, any problem with the refrigerant flow, will affect the pressures. So keep your eyes open for any change.

    If there is a doubt, don't mess with it and replace it.
    Cap tube systems require experience and patient.

    Chemi

  4. #4
    Join Date
    Oct 2005
    Location
    kent , england
    Posts
    27
    Rep Power
    0

    Re: Flogging a dead horse.

    i have found that the best way of diagnosing this problem is to run the unit with your suction gague fitted , if there is a blockage or if the system is short of gas ,the system will behave in the same manner by pumping to a low pressure or even a vacume , hovever , if you switch the unit off , if there is a blockage at the cap or drier the suction pressure will stay where it is or rise very slowly, whereas if the system is just short of gas, the pressure will rise to at least 0 psi quite quickly, also when the unit is switched off if there is a blockage the drier or cap will get v cold or even start to ice up which will not happen if the unit is just short of gas
    chill out it's only a fridge

  5. #5
    Join Date
    May 2005
    Location
    manchester
    Age
    49
    Posts
    48
    Rep Power
    0

    Re: Flogging a dead horse.

    i have to agree with shanes696
    like people have said in the past caps can be very tricky at times and take time to diagnos properly with plenty of patience.
    i would go about it the same switching off the unit and checking the reaction of pressures also temp of copper drier etc.
    i was going to put this point forward last night but i was interested to see how other people deal with this situation.
    as sombody on the site says better to keep quiet and look stupid than speak up and remove all doubt.
    but yes this is how i usally deal with this diagnosis would anybody else like to agree or advise on other methods.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Flogging a dead horse.

    You were calling me?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  7. #7
    Join Date
    May 2005
    Location
    manchester
    Age
    49
    Posts
    48
    Rep Power
    0

    Re: Flogging a dead horse.

    thats the one peter good phrase i like that one

  8. #8
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Flogging a dead horse.

    Thanks for your replies people.I have taken it on board.

    The reason I started this thread was I was working on a freezer which I suspect of a blocked capillary.

    Some information.
    Model:Zannoti slide in BGM220394.
    Compressor:Hermitique FH2480Z.
    Refrigerant:404A
    Hot gas defrost.

    Upon arriving at job check all coils evap and condenser were clear.
    Suction Pressure:15psi
    Room temp: -12 degrees c
    Suction line temp just before comp -4.4 degrees c.

    Initially thought that unit was short of refrigerant but after looking and not finding a leak tried adding refrigerant but situation did not improve. Then I suspected a restriction.

    Reclaimed charge and evacuated.Then weighed in nameplate charge (0.84kg). After weighing in.
    Suction Pressure:14psi
    Room temp: -14 degrees c
    Suction line temp just before comp: -4.3 degrees c.

    At that room temp the suction pressure should be higher. Therefore the only conclusion is a restriction.

    Any help would be appreciated.

  9. #9
    Join Date
    Sep 2005
    Location
    Singapore
    Age
    59
    Posts
    145
    Rep Power
    19

    Re: Flogging a dead horse.

    A restricted cap tube causes the condenser coil flooded with liquid, will have a higher condensing pressures and higher compressor running amperes.

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Flogging a dead horse.

    No, it wont.
    Think why.

    Chemi

  11. #11
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Flogging a dead horse.

    Hi Temprite,

    Ive had one of those zannoti`s do this as well, and I found it short of gas.
    I know the nameplate says what it says but I checked my capillary and it was ok.
    I just charged the thing untill it 'felt' right and all was ok.

    Dont forget to check the evap fan direction and if the blade is on the right way.

    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  12. #12
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Flogging a dead horse.

    Quote Originally Posted by Temprite
    Refrigerant:404A
    Hot gas defrost.

    Upon arriving at job check all coils evap and condenser were clear.
    Suction Pressure:15psi
    Room temp: -12 degrees c
    Suction line temp just before comp -4.4 degrees c.


    Reclaimed charge and evacuated.Then weighed in nameplate charge (0.84kg). After weighing in.
    Suction Pressure:14psi
    Room temp: -14 degrees c
    Suction line temp just before comp: -4.3 degrees c.

    Any help would be appreciated.

    Im thinking on this one
    Its not a restriction I dont think
    If it was a restriction you would be in vacuum
    I know, youre thinking , maybe its a partial vacuum

    Your back pressure 15psi is correct
    This is my advice

    Switch off your evaporator fans
    Add refrigerant till the whole evaporator coil is iced
    At this point stop adding refrigerant

    Make sure your condensor coil is clean

    See how it goes
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  13. #13
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Flogging a dead horse.

    No one yet has mentioned checking the compressor running current - it's a must when charging a system.

    Too little refrigerant and low amps, too much refrigerant and high amps. All part of the overall picture.

  14. #14
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Flogging a dead horse.

    Yes Frank, But if there is a partial blocked cap tube, then your amps will not show the truth.

    Chemi

  15. #15
    Join Date
    Jul 2002
    Location
    Stamford, CT USA
    Age
    46
    Posts
    74
    Rep Power
    22

    Re: Flogging a dead horse.

    What works best for me is something I picked up off this forum. A restriction in the liquid line will have an initial high pressure (liquid), at start up or when adding gas in an attempt to compensate for the low suction. then it will work its way down. Lots of sub cooling, usually cold drier.
    John K.

  16. #16
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Flogging a dead horse.

    Just an update.

    Turns out chillin was right.

    After checking capillary and weighing in charge system was still short.

    Nameplate 0.84kg.

    System took about 1.15kg but I also installed slightly larger dryer.

    Working much better.

    Suction pressure about 24 Psi.]

    Thanks all for your valuable comments.

  17. #17
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Flogging a dead horse.

    Quote Originally Posted by Temprite
    G'day all

    Does taking the temperature in the mid point of the condenser coil give you a proper indication of SCT good enough to do a subcool measurement?

    Thanks in advance.

    Try using a small piece of cardboard. Poke a hole in the center for your temperature sensor and hold the cardboard against the condenser fins to block airflow around the sensor. This will give you a more accurate estimate of SCT.

  18. #18
    rbratlett's Avatar
    rbratlett Guest

    Re: Flogging a dead horse.

    generally using a surface probe on any of the u bends around the coil's middle third will give you an indication of saturation temperature.

  19. #19
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Flogging a dead horse.

    Thanks for the tip Gary.

    Richard.
    I have a pipe clamp, a wire bead, and a digital thermometer. Good contact thermometer is next on the shopping list.

Similar Threads

  1. compressor horse power
    By ewart in forum Industrial Compressors
    Replies: 9
    Last Post: 27-07-2009, 05:39 PM
  2. Horse power rating
    By Argus in forum Air Conditioning
    Replies: 0
    Last Post: 03-02-2005, 10:52 AM
  3. motor horse power
    By mtoto in forum Fundamentals
    Replies: 4
    Last Post: 05-06-2002, 03:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •