    Re: Flogging a dead horse.

    Quote Originally Posted by Temprite
    Refrigerant:404A
    Hot gas defrost.

    Upon arriving at job check all coils evap and condenser were clear.
    Suction Pressure:15psi
    Room temp: -12 degrees c
    Suction line temp just before comp -4.4 degrees c.


    Reclaimed charge and evacuated.Then weighed in nameplate charge (0.84kg). After weighing in.
    Suction Pressure:14psi
    Room temp: -14 degrees c
    Suction line temp just before comp: -4.3 degrees c.

    Any help would be appreciated.

    Im thinking on this one
    Its not a restriction I dont think
    If it was a restriction you would be in vacuum
    I know, youre thinking , maybe its a partial vacuum

    Your back pressure 15psi is correct
    This is my advice

    Switch off your evaporator fans
    Add refrigerant till the whole evaporator coil is iced
    At this point stop adding refrigerant

    Make sure your condensor coil is clean

    See how it goes
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,667
    Rep Power
    51

    Re: Flogging a dead horse.

    No one yet has mentioned checking the compressor running current - it's a must when charging a system.

    Too little refrigerant and low amps, too much refrigerant and high amps. All part of the overall picture.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Flogging a dead horse.

    Yes Frank, But if there is a partial blocked cap tube, then your amps will not show the truth.

    Chemi

Similar Threads

  1. compressor horse power
    By ewart in forum Industrial Compressors
    Replies: 9
    Last Post: 27-07-2009, 05:39 PM
  2. Horse power rating
    By Argus in forum Air Conditioning
    Replies: 0
    Last Post: 03-02-2005, 10:52 AM
  3. motor horse power
    By mtoto in forum Fundamentals
    Replies: 4
    Last Post: 05-06-2002, 03:32 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •