    69L drop in...??????



    Hello, I have an existing freezer room running on R69L. I am still a bit short on charge and have no 69L left. Is there any other refrigerant that I can drop in on top it...????
    Thanks Scooter.



  2. #2
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: 69L drop in...??????

    we use 422 or oil change and 404a it

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: 69L drop in...??????

    Short answer is NO. You shouldn't mix refrigerants without full knowledge of what you are mixing.

    You could replace it though.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,092
    Rep Power
    33

    Re: 69L drop in...??????

    69l is a drop in for r502 i think,so recover it all send it for recycling then oil change ,flush triple vac recharge with 404a,and i would change oil again after one week of running of coarse change the filter drier,any suction core filters drain oil sep etc,bottom line is a big job best of luck,first thing to check is are you certain its short of refrigerant?.