Results 1 to 4 of 4
Thread: 69L drop in...??????
-
22-06-2011, 07:06 AM #1
69L drop in...??????
Hello, I have an existing freezer room running on R69L. I am still a bit short on charge and have no 69L left. Is there any other refrigerant that I can drop in on top it...????
Thanks Scooter.
-
22-06-2011, 07:39 PM #2
Re: 69L drop in...??????
we use 422 or oil change and 404a it
-
22-06-2011, 11:25 PM #3
Re: 69L drop in...??????
Short answer is NO. You shouldn't mix refrigerants without full knowledge of what you are mixing.
You could replace it though.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
23-06-2011, 12:50 AM #4
Re: 69L drop in...??????
69l is a drop in for r502 i think,so recover it all send it for recycling then oil change ,flush triple vac recharge with 404a,and i would change oil again after one week of running of coarse change the filter drier,any suction core filters drain oil sep etc,bottom line is a big job best of luck,first thing to check is are you certain its short of refrigerant?.