    Loading and Unloading of chiller

    Dear Friends ,

    As we already know that when we start the chiller , it takes sometime to come on full load i.e 100 % . Can you please tell me what are the main reasons due to which chiller is not initially started (put) at full load i.e 100 %. Why it usually starts with 10-20-40-50 % and so on.

  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Loading and Unloading of chiller

    Power consumption, letting the compressor start efficiently,
    Imagine starting your car and putting it in 5th gear and trying to pull away it wouldn't be easy

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: Loading and Unloading of chiller

    Good answer James!
    Grizzly

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Loading and Unloading of chiller

    also to prevent short cycling and allow for better control

  5. #5
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Loading and Unloading of chiller

    Thanks james for your reply.

    Hi Install Monkey ,

    Can you please explain me how it can prevent short cycling.

    Thanks for your cooperation

  6. #6
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    52
    Posts
    2,549
    Rep Power
    24

    Re: Loading and Unloading of chiller

    Lower inrush current

  7. #7
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: Loading and Unloading of chiller

    Hi Sumit
    If you start say a building on a cold morning and there is an initial heat load due to office and internal heat sources - all or most of the chilled water valves CHWVs will open at near 100% then they would close in about 1/2 an hour, this would mean the chiller goes to 100% for a short time and then there would be no load due to use of outside air as a first stage of cooling. Where the outside air cooling would be enough to bring the building down to temp in 1 hour. Considering most commercial buildings are charged for power on the highest 1/2kWh for the whole month where it is possible that the chiller may not be required for that month.
    The chiller load on stage up is often controlled by deviation from CHW setpoint plus a time of say 20 mins (depending on the size of the system). If you had a load of 100kW and your chiller is 500kW at 100%loading it would start then shut down and start again in short periods of time.

  8. #8
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Loading and Unloading of chiller

    Thanks Tesla,