    Flow Rate of water



    Dear Friends ,

    Is there any standard formula to calculate the ideal flow rate of water in the condenser or chiller pipeline ? I have somewhat idea regarding the same but not sure.

    I hope you will share your ideas.

    Thanks for cooperation.



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Flow Rate of water

    Hello sumit,
    the majority of water chillers and water cooled condensers are based on 5.5'C temp rise.
    Apply formula for water chilling ; Kw = 4.2 Kj/kg * temp rise [ 'C ] * flow rate in Litres per second.
    Flow rate = Kwr / 4.2 / 5.5 'C example
    160Kw r / 4.2 / 5.5 = 6.93 litres per sec.
    Reduce the temp rise and flow rate will increase.

  3. #3
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Flow Rate of water

    Dear Magoo ,

    Thanks a lot for your reply. According to you , Flow Rate = KWr / 4.2 / Temp Rise. Can you please again explain me this formula , as i am not able to get the meaning of Kwr. I know what is temp rise , but please explain me other terms used in this formula. I will be thankful to you.

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Flow Rate of water

    Kw refrigeration as opposed to Kw electrical

  5. #5
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Flow Rate of water

    kw/ 4.2 x dt = kg/s or L/s for water

    kw = energy absorbed through refrigeration
    4.2 = specific heat capacity of water ( kj/kg )
    dt = temp in and out ( k )
    fridge

  6. #6
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Flow Rate of water

    Hi Fridge ,

    Thanks for your reply.

    According to you , flow rate (L/S) = KW / 4.2 * dt.

    But Magoo's formula was different , he said Flow rate (L/S) = KW/4.2/DT

    Which one is correct ?

  7. #7
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Flow Rate of water

    well the formula is derived from:

    Q = m x cp x dt hence m = Q/ cp x dt

    where Q = capacity in (KW)
    m = mass flow rate ( kg/s or L/s)
    cp = specific heat capacity ( kj/kg)
    dt = temp difference (k)

    so its a simple transposing of the original formula
    fridge

  8. #8
    Join Date
    Aug 2011
    Location
    West yorkshire
    Age
    37
    Posts
    10
    Rep Power
    0

    Re: Flow Rate of water

    Quote Originally Posted by FRIDGE View Post
    well the formula is derived from:

    Q = m x cp x dt hence m = Q/ cp x dt

    where Q = capacity in (KW)
    m = mass flow rate ( kg/s or L/s)
    cp = specific heat capacity ( kj/kg)
    dt = temp difference (k)

    so its a simple transposing of the original formula



    Hi Fridge,
    Thanks a lot for sharing the above formula about flow rate of water. I already have services to audit water leaks and techniques to detect them properly, but I want to know more about water audit services which can be helpful to save water and water bill. Can you tell me that this formula related with flow rate of water is useful or not to water audit services.
    Please share your ideas and tell about other more water audit services to save water and cost money.

    Thanks
    Maire

  9. #9
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Flow Rate of water

    Hello Sumit
    The equipment specifications dictate which flow rates are necessary for the equipment normal functioning. Note that savings on water in this respect may lead to your lost of the equipment.

  10. #10
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Flow Rate of water

    Hi Maire,

    If by water audit you mean water treatment or rate of water lost, then this formula will not help. I have no experience in water treatment but regarding the leakage rate/ evaporation rate, i think it may be worth looking at the cooling tower drift eliminators. Over the years they deteriorate and allow more than the normal amount of water lost through evaporation and increase your water bill. Good water treatment can reduce this deterioration also.
    I've heard of companies doing eliminators that can reduce the rate of water lost through evaporation in cooling tower. If you can reduce the rate of evaporation water loss without sacrificing the towers heat rejection capacity then you may make savings on your water bill.
    fridge

  11. #11
    Join Date
    Aug 2011
    Location
    West yorkshire
    Age
    37
    Posts
    10
    Rep Power
    0

    Re: Flow Rate of water

    Quote Originally Posted by FRIDGE View Post
    Hi Maire,

    If by water audit you mean water treatment or rate of water lost, then this formula will not help. I have no experience in water treatment but regarding the leakage rate/ evaporation rate, i think it may be worth looking at the cooling tower drift eliminators. Over the years they deteriorate and allow more than the normal amount of water lost through evaporation and increase your water bill. Good water treatment can reduce this deterioration also.
    I've heard of companies doing eliminators that can reduce the rate of water lost through evaporation in cooling tower. If you can reduce the rate of evaporation water loss without sacrificing the towers heat rejection capacity then you may make savings on your water bill.
    Hi Fridge.....

    Thanks a lot for the for such a kind and helpful reply..... I hope that might help me out some what...... Once again thanks a lot.....

  12. #12
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Flow Rate of water

    Hello

    Water is supposed to evaporate in a cooling tower, and the more, the better. To achieve the same effect without evaporation, one need to move more volumes of water, but by that more energy is spent on pumps.

    If ,for instance, to keep a condensation T at a T a water condenser is designed for there is need for a definite amount of the coolant, one cannot be happy with an economy he/she has achieved on water on expense of the equipment life.

  13. #13
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Wink Re: Flow Rate of water

    Hello Yuri B,

    Yes you are correct, but you can make water savings by combining sensible and evaporative heat transfer.

    http://www.baltimoreaircoil.be/BAC/EU/axidownloads20.nsf/activedocuments/115FF044BDFE4B49C125709D00537C2F/$FILE/BAC%20Intelligent%20Water%20Saving%20Products.pdf

    anyway dont worry, i think the person who asked the question is actually trying to sell something on here
    fridge

  14. #14
    Join Date
    Oct 2009
    Location
    Malaysia
    Age
    37
    Posts
    16
    Rep Power
    0

    Re: Flow Rate of water

    Hi sumit,

    In order to get flow rate of chilled water or condenser water for centralized chiller plant, there are 3 ways to do it:

    1) By using flow meter - result: very accurate reading
    2) By using formula or calculation of Chiller Capacity (Q = m x Cp x delta T) - result: not much accurate
    3) By using pump (either CHWP or CDWP) performance curve. Once u get the delta Pressure (Outlet Pressure - Inlet Pressure), use the pump OEM to plot the flowrate reading - result: accurate

  15. #15
    Join Date
    Apr 2011
    Location
    India
    Age
    36
    Posts
    94
    Rep Power
    13

    Re: Flow Rate of water

    HI,

    Thanks Yuri, Fridge , Maire and schiZOprEni for your replies. schiZOprEni , can you please explain the third method to calculate flow rate.After getting the delta pressure of pump, how can one plot the flow rate reading ? What is OEM.

    Thanks for your cooperation.

  16. #16
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: Flow Rate of water

    Btu/hr
    flow rate (us gpm ) = -----------------------------------------------------
    500 x water temp out deg f - water temp in deg f

  17. #17
    Join Date
    Aug 2008
    Location
    Baltics
    Age
    62
    Posts
    786
    Rep Power
    16

    Re: Flow Rate of water

    The more water flow is through the pump, the more work does its el. motor, the more ampers are consumed by it. You can look at what the pump (motor) maximal current is - by its maximal capacity, according to its specification - and what ampers the pump goes now with, then comparing you can see more or less what at this moment flow rate may be.
    Last edited by Yuri B.; 24-08-2011 at 06:03 PM.

  18. #18
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Flow Rate of water

    OEM = original/official engineering/equipment manufacturer

  19. #19
    Join Date
    Oct 2009
    Location
    Malaysia
    Age
    37
    Posts
    16
    Rep Power
    0

    Re: Flow Rate of water

    Hi Sumit,

    Pump performance chart/graph is given by the manufacturer (OEM) once a pump is tested at their lab. It is just like a birth certificate. On the graph, there are two parameters Total Head (or delta Pressure) at the Y-axis and Total Flow Rate (USGPM) at the X-axis. As i said, once u get the value for delta Pressure across a Pump, then u can measure the liquid flow rate by plotting the point on the graph.

  20. #20
    Join Date
    Nov 2007
    Location
    colchester
    Age
    43
    Posts
    10
    Rep Power
    0

    Re: Flow Rate of water

    a easy way is by looking at your pumps info - min and max head. if it says e.g - 4.2 min and 6.8 max you can take on the middle i.e about 5.5 bar. Or they may say 42 headmin 68 head max just remember they mean 4.2 not 42 bar. Head is up. bar is flow. to commission these you may need to slow the head pressure or increase which may require a bypass. Plus make sure pump amps are right. There are a lot of graphs that are easy to read per manufacturer