    PH level of water and chemical solution - Descaling



    Dear Friends ,

    How much PH value of solution of water and chemical should be maintained while doing the De-scaling of condensers. If the solution is more acidic , it will damage the copper tubes and if its less then will not remove the scale effectively.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: PH level of water and chemical solution - Descaling

    I think that it may depend on the product being used, the following link refers to a particular brand but shows PH levels between 0.5 and 0.7 for the different options.

    Perhaps ask your chemical supplier.
    http://descale.me/downloads/document...Exchangers.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    400
    Rep Power
    18

    Re: PH level of water and chemical solution - Descaling

    While plant operates , maintain the following parameters to avoid regular de-scaling

    1) maintain alkaline ph .. 7+
    2) address dissolved oxygen issue by additives ...... To avoid tubes pitting
    3) maintain commercial hardness of cooling water around 5
    4) provide tower bleed-off
    5) maintain tower hygene

    this will give you exceleent results on condenser life & plant perfformance . This will avoid sudden failures