    Just wondering what the rule of thumb is with glass door freezer superheat. I have seen cases specified at 5k and flood back badly. I was told 10k but wanted to hear others opinions.
    Thanks



  2. #2
    S.Palvi (jnr)'s Avatar
    S.Palvi (jnr) Guest

    Re: Glass door freezer superheat

    Usually 5-7K yes, but if the compressor is situated lower than the blower coil remember a trap higher than the coil to prevent flooding. (asuming the coil is clean and optimal airflow is achieved)

  3. #3
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Glass door freezer superheat

    When you say flood back badly, is it just ice on suction of compressor, or is there a measured value of low/no superheat combined with other indicators such as cold discharge temperature and noises from compressor? As suggested in previous post, SH 5 - 7 DegK is normal, but often results in frost at the compressor - sometimes mistaken for floodback. Typical freezer systems normally have suction accumulator to provide some degree of liquid protection.

  4. #4
    Join Date
    Jan 2009
    Location
    Sydney
    Age
    44
    Posts
    58
    Rep Power
    16

    Re: Glass door freezer superheat

    Not sure whether this rack has an accumulator. Thanks for your input I will try and lower all superheat on all the freezers and see how the system runs.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Glass door freezer superheat

    Hi Fridgy Dave.
    do a forum search on superheat, there is a lot of discussion on subject to read.
    magoo

  6. #6
    Join Date
    Jan 2009
    Location
    Sydney
    Age
    44
    Posts
    58
    Rep Power
    16

    Re: Glass door freezer superheat

    Thanks magoo I'll check that out

  7. #7
    S.Palvi (jnr)'s Avatar
    S.Palvi (jnr) Guest

    Re: Glass door freezer superheat

    Quote Originally Posted by HVACRsaurus View Post
    When you say flood back badly, is it just ice on suction of compressor, or is there a measured value of low/no superheat combined with other indicators such as cold discharge temperature and noises from compressor? As suggested in previous post, SH 5 - 7 DegK is normal, but often results in frost at the compressor - sometimes mistaken for floodback. Typical freezer systems normally have suction accumulator to provide some degree of liquid protection.
    This is quite true, a colder discharge temp and a cold oil sump usually means liquid. A small SH of below 5 whould be the first indication of liquid overshooting, but also as Gary the VIP mentioned there is alot of factors that needs to be balanced out.