    Smile Panel frick quantum lx



    Hello boys:

    I'm doing a retrofit electric RXF39 packaged, including quantum micropanel a linear potentiometer. to raise the energy I get the following warning:

    slide valve low warning!

    that causes this alarm



  2. #2
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15

    Re: Panel frick quantum lx

    Did you use the new style slide valve potentiometer which is enclosed with a Hirshman connector for the wiring or did you use the old style black linear potentiometer which mounts on a teflon block and the wires are soldered directly to the potentiometer?

  3. #3
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Panel frick quantum lx

    the new style of potentiometer

  4. #4
    Join Date
    May 2008
    Location
    Virginia
    Age
    46
    Posts
    8
    Rep Power
    0

    Re: Panel frick quantum lx

    The old style sensor was a 1-5 VDC potentiometer, the new style sensor you have installed is a linear position indicator that outputs a 4-20Ma signal I believe. Go to session 2 or 3, then go to calibration , select capacity/ volume, then under signal source or type you can select from a 1-5 vdc, 4-20 Ma, pot, and a couple others. If you select the 4-20Ma then do an auto calibration you should be good. These micro's are a pain in the butt!

  5. #5
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Panel frick quantum lx

    I was reviewing all the settings and saw that does not show the number of steps to the potentiometer