    Calorex AW910ALX Heat Pump Cable question



    Hi
    Just received a second hand Calorex AW910ALX Heat pump. Details in the manual say Max Supply Fuse amp is 25, Max running is 15. What cable do I need to connect it to the circuit breaker (the breaker is 30amp is that OK)?

    thanks



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Calorex AW910ALX Heat Pump Cable question

    recommend 6mm to be on the safe side.as when the unit kicks in there is a big surge on start up and u will have a good earth conductor. unless the unit is miles away from the board

  3. #3
    Langy3366's Avatar
    Langy3366 Guest

    Re: Calorex AW910ALX Heat Pump Cable question

    like this?
    http://www.tlc-direct.co.uk/Products/NY6slash3.html
    Unit is 5m from the board.

  4. #4
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Calorex AW910ALX Heat Pump Cable question

    steel wired armoured cable would be better as the steel braiding protects the cable and it is more robust.and use an outdoor gland pack as to reduce the corrosion effect of high humidity and chlorine.

  5. #5
    Join Date
    Mar 2008
    Location
    England
    Age
    68
    Posts
    250
    Rep Power
    17

    Re: Calorex AW910ALX Heat Pump Cable question

    Unless you are a "compentant person" you should have a qualified electrician do this work (or at least check it afterwards) - especially if this is a domestic installation where a Part P qualified electrician will be required.
    6mm2 SWA with gland kit should be OK if the cable is being burried or, a toughened / impact resistant PVC cable if overground which can be used with plastic stuffing glands.
    You also need to get the right type of circuit breaker for a DOL non inverter system which will have a high starting current. It may run at 15amps but the starating current will way higher for a split second. The existing 30amp breaker may not be the right type. Again an electrician would know what type to supply & fit.
    If in doubt read the instructions. If still in doubt follow them.