Thread: Condensing temp of refrigerant
02-10-2005, 08:23 AM #1
In Air Source Heat Pump, where the condensing medium is water, to get hot water at 60 deg. C., what should be the condensing temp of refrigerant?
02-10-2005, 05:53 PM #2
Re: Condensing temp of refrigerant
Hello Anup. If you want to get hot water at 60 deg. C the condensing temperature of refrigerant must be bigger then the temperature of water. 64-66 deg. C should do it.
Best wishes.
02-10-2005, 10:18 PM #3
Hi Anup , in any heat exchanger , to heat a substance at least you need the tempreture of the heating substance to be the desired tempreture of the heated substance + .
Like if you want to heat water from 10*C to 20*C , at least you need a heat source of 21*C .
The capacity should also be calculated , I mean you can't heat 10 Kg of water from 10 to 20*C with 5Kg of water at 21*C .
The same principle applies to your questionEngineering, sciences, math, physics and my brain will generate "not responding " soon
04-10-2005, 06:51 AM #4
Hi anup
it will depend on your heat exchanger design. Usullay 3~5K is the lower limit. Too small temp diff will cause bigger size heat exchanger and increase cost.
rgds
LC
04-10-2005, 03:14 PM #5
Hi, How to calculate over all heat transfer co-efficient for a eveporator and how does it corelated with tube thermal conductivity ?
CARE refigerants by BOC
By dogma in forum RefrigerantsReplies: 8Last Post: 23-03-2010, 12:39 PM -
Air Source Heat Pump - temp of refrigerant leaving evaporator
By anup in forum FundamentalsReplies: 3Last Post: 06-11-2006, 05:04 AM -
Condensing temp in refrigeration
By anup in forum FundamentalsReplies: 1Last Post: 02-10-2005, 11:18 AM -
condensing temp rule of thumb
By angryk in forum FundamentalsReplies: 8Last Post: 14-03-2003, 04:00 AM -
Which refrigerant to use for low temp apps?
By DaBit in forum Technical SpeculationsReplies: 14Last Post: 21-09-2002, 03:17 PM