    18000btu aricon



    Hi Guys,

    I have a 18000btu split unit, the condenser fan is not working on cooling cycle,
    the compressor comes on, the solenoid has power, the indoor blows.

    i have changed the capacitor, the p.c. board & electrical board, but this does not help,
    i tested the unit in heating mode, the fan comes on immediately & seems to operate
    ok, problem is i cannot fill with gas to the right pressure?

    any ideas out there?



  2. #2
    mundow1's Avatar
    mundow1 Guest

    Re: 18000btu aricon

    If you already changed the pc board then check and/or change the condenser temperature sensor.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: 18000btu aricon

    Does the fan have a multi-speed motor? If so check all of the windings, maybe the cooling side uses different winding to the heating cycle.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    770
    Rep Power
    19

    Re: 18000btu aricon

    hi draco,
    are you weighing in the gas , then can you not gas it up on heating mode? sedgy ,

  5. #5
    Join Date
    Nov 2008
    Location
    scotland
    Age
    74
    Posts
    232
    Rep Power
    16

    Re: 18000btu aricon

    gas dischage temp switch on the subcooled line ??
    DM

  6. #6
    Join Date
    Sep 2009
    Location
    Gauteng
    Age
    51
    Posts
    16
    Rep Power
    0

    Re: 18000btu aricon

    Hi Guys,
    thanks for the replies, it seems the unit had a gremlin inside! if i replace the electrical components one by one + the sensors, the unit fan still does not operate, when i replace all the components together, the unit runs 100%
    i have tested now for a whole day on heating & cooling, no problems.
    thanks for all you help!

  7. #7
    Join Date
    Aug 2010
    Location
    England
    Age
    53
    Posts
    77
    Rep Power
    16

    Re: 18000btu aricon

    Its a dart art, to be sure