    Sep 2005
    India
    49
    30
    Question Air Source Heat Pump - temp of refrigerant leaving evaporator
    Hi Technocrats,
    I am trying to design air source heat pump for water heating application. Though I have an experience in selling heat pump, but not designed nor have information.
    Cosider the example:
    Refrigerant-R22
    Evaporating temp - 4 deg. C. (39.2 F)
    Ambient air temp (flowing through evaporator) - 30 deg. C (86 F)
    Temp drop across evaporator - 7 deg. C. (44.6 F)
    My query:
    1. How to design evaporator?
    2. How to calculate heat content in refrigerant gas at evaporator outlet?
    3. How to calculate, refrigerant gas temp leaving evaporator?
    Sep 2003
    ISRAEL
    72
    4,248
    Re: Air Source Heat Pump - temp of refrigerant leaving evaporator
    Hi anup,
    I am not a designer but a welded plate HE is the best for your application.
    You will need to provide more details if you want some free advice, like, information on the water side.
    Chemi
    Sep 2005
    India
    49
    30
    Dear Chemi,
    Thanks for your reply. I was coming to that point but at a later stage.
    Water part will come while designing condensor. but before that I need to understand evaporator design, based on which I can give you heat content in discharge gas (from compressor).
    Meanwhile, could you pl. give some basic guidelines for condensor?
    Anup
    Nov 2006
    Australia
    59
    14
    hi Anup,
    How many litres of water are you heating? will the water be in a insulated storage tank? how many kiloWatts compressor capacity do you require to heat the water, what is your cut in / cut out water temperature degrees C? The problem you may find is that up to a certain water temperature, Eg. up to 40 degrees C condensing the refrigerant is not a problem, after that the condensor may become just a subcooler and therefore the eficiciency or COP of your system will fall very quickly.
  1. dual source heat pump
    Last Post: 12-08-2010, 02:24 AM
  2. frostles heat pump
  3. Ground source heat pump
    By Cooler in forum Domestic
    Last Post: 29-07-2006, 08:51 PM
  4. Evaporator Design-Air Source Heat Pump for water heating
    By anup in forum Technical Discussions
    Last Post: 20-03-2006, 02:26 PM
  5. Mcquay water source heat pump
    By bernie in forum Air Conditioning
    Last Post: 10-02-2003, 01:53 AM