    Mitsubishi Heavy SRK/SRC20ZJX-S test mode / pumpdown



    Hi guys,

    I am seeking for information as how to enable test mode for forced cooling on a small Mitsu SRK of the latest SRK hyper inverter series.

    Usually I expect to find some kind of notice about it in the service manuals, but I had little luck with both the technical manual and the data book.

    I would appreciate if you have any ideas on that.

    Thanks a lot,
    -Dave



  2. #2
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: Mitsubishi Heavy SRK/SRC20ZJX-S test mode / pumpdown

    9) Test run

    a) For a test run, it is possible to use the dip switches SW5-3 and SW5-4 on the printed circuit board in the outdoor unit.

    b) Test run time is 30 minutes. Protective devices are effectively controlled.
    sw 5 4 OFF Test run for cooling
    sw5 4 ON Test run for heating
    sw 5 3 on to initiate test mode



  3. #3
    Join Date
    Aug 2008
    Location
    germany
    Posts
    34
    Rep Power
    0

    Re: Mitsubishi Heavy SRK/SRC20ZJX-S test mode / pumpdown

    Thanks a lot! That's just what I was looking for.

    Is there any service manual / data book I have missed?

    Cheers,
    -Dave