    Emerson ZXE Refrigeration Units



    I am having issues with the Condenser fans on 2 Emerson ZXE units,,,one is the 600 and the other is a 750.The condenser fans continually shut down even on 400psi head pressure and will not restart.
    Two of the fans had burnt out a year ago and replaced and still the fans shut down and the compressor goes out on high head pressure and requires a restart(turn off isolator and reset)Both Units are on R22,,,-5C SST
    Are these a bucket of S,,it or is there a fix,,,,,hope someone has come across this.
    Thanks
    Lawrie


    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Emerson ZXE Refrigeration Units

    Are the fan pressure switches wired up correctly?
    Brian - Newton Abbot, Devon, UK