15-05-2011, 12:24 PM #1
Just registered in, thus newbie. RE's real knowledge reservoir. Great people.
Hi all, Is it possible to convert temperature to pressure units?
For instance, attach a pt100 temperature sensor onto the discharge piping. retrieve the read temperature data and convert to discharge gas pressure reading.
Please advise.
thks
15-05-2011, 07:00 PM #2
Re: Just registered in, thus newbie. RE's real knowledge reservoir. Great people.
this will not ive you gas pressure as the discharge is superheated gas not saturated refrigerant
16-05-2011, 04:07 AM #3
Hi kkwong.
welcome to the forum.
You will need a pressure transducer. Not a PT100.
16-05-2011, 10:12 AM #4
Glad to know you and thks for your prompt reponse.
Hi Martin, I'm rather agreed with you. even by simply mesuring any vapour mmHG at a 100C boiling point, it gave only 760 (29.92HG) = 14.7 psi, it's far beyond the refrigerant discharge pressure which usually read 200-200 psi (R22). The reason I ask this question is that in my area, people used to say that it's possible to convert temperature reading into pressure reading, but I don't know how they do that. I think it's a myth.
Hi Magoo, thks your your welcome msg. Actually my previous question above was a decoy, sorry!. The true story was: I'm currently developping a PLC based test control system with local and remote scada. I already have Tecsis pressure transducers to measure discharge/suction pressures, but I have also wanted to measure the compressor's oil pressure. Unfortunately I have only a small rack configuration: 3 units of 2hp hermetic compressors (for c.modulation). As you can imagine, it's almost impossible to find dispositive i.e oil pump or nipple installed allowing to fix a pressure transducer on such smal hp compressor (even for semi-herm nowdays). This is the reason why I was looking for alternative means to overcome this issue.
Suggestions and advises from you guys would be highly appreciated.
thanks a lot again Martin and Magoo
Have a nice day.
14-07-2011, 07:02 PM #5
Kkwong0: If you had the space, the NOSHOK 755 would be perfect for you, because it allows you to measure pressure and temperature at the same time with high accuracy. Look here: http://www.noshok.com/755-756_series.shtml
It is very expensive and too big though. Probablyh made for more industrial applications. Anyway, you have Tecsis...they seem to be partners with Noshok, and I have worked with both companies. Give Noshok a shot, they are americans, not germans, meaning they know how to help and sell you the right products!