    Bad TXV ? or solenoid valve?



    i have a AC unit around not sure of tons but i would guess 15 ton, runs on R22..... it has 1 compressor but 2 stages at the evap. coil.

    each 1/2 of coil has its own TXV and a solenoid valve just before the TXV.

    i am getting flow and cooling through the 2nd stage of coils, The solenoid valve is opening and the txv is operating.

    But the 1st stage is doing nothing, i have power 24v to solenoid and the magnet is working but im not sure its opening, there is a manual screw on the bottom of the solenoid valve that i screwed all the way in to force it open, still nothing........

    could it still be the solenoid it stuck shut? or is my TXV not operating? and staying shut???



  2. #2
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Bad TXV ? or solenoid valve?

    hi
    you should start from the filter drier may be restriction is there.
    about solenoid valve when its energized you should hear a click .

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Bad TXV ? or solenoid valve?

    Hi Kurt S
    if the power element on the TXV looses its charge it will shut the TXV down, zip zero flow.

  4. #4
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    52
    Posts
    1,083
    Rep Power
    23

    Re: Bad TXV ? or solenoid valve?

    Hi Kurt
    I think Magoo is right - the TXV blocked or element has lost charge. If you have a conventional solanoid valve you could use a permanent magnet to check. I have had one that would click but didn't open til I put on the magnet which kept a chiller going until I got a new solanoid valve. Considering there should be only one drier and the other circuit is flowing. If there was a little flow at start up it would suggest moisture in the system. I would simply replace the drier and TXV.

  5. #5
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Bad TXV ? or solenoid valve?

    I would disconnect the working circuit and check if the suction pressure increases when SV energize.
    Filter in the TXV entrance should be checked too.
    If nothing work, start with replacing the TXV, SV does not have as many problems as TXV.

    Basically I am with Magoo direction.

  6. #6
    Join Date
    Sep 2008
    Location
    usa
    Posts
    27
    Rep Power
    0

    Re: Bad TXV ? or solenoid valve?

    thanks for the responses ill keep you updated, the SV has a manual screw for a bypass on the bottom i also tried and still nothing. i assume its the txv, i will take it apart and find out next week.

    as for the dryer it is just before both of the valves as TESLA mentioned so that is not the problem.

    thanks so far, im sure it will get worse before it gets better.

  7. #7
    Join Date
    Feb 2009
    Location
    USA
    Age
    54
    Posts
    143
    Rep Power
    16

    Re: Bad TXV ? or solenoid valve?

    Did you find the second compressor?

  8. #8
    Join Date
    Sep 2008
    Location
    usa
    Posts
    27
    Rep Power
    0

    Re: Bad TXV ? or solenoid valve?

    Royal241
    Re: Bad TXV ? or solenoid valve?
    Did you find the second compressor?




    not yet yet what do they look like?

    for anyone else interested (that actually cares) ill keep you updated. going to have to wait 2 weeks for new txv..... and new toy http://store.cyberweld.com/smqutwtip.html

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Bad TXV ? or solenoid valve?

    Hi Kurt.
    with most TXV's Danfoss Sporlan Alco, you can purchase the power element assembly as an individual item. Probably too late if you have ordered a total new TXV.
    Keep us informed with results though.

  10. #10
    Join Date
    Sep 2008
    Location
    usa
    Posts
    27
    Rep Power
    0

    Re: Bad TXV ? or solenoid valve?

    i installed the new tev and its working much better, is changing the power head easy to do? the old one looked like it was brazed to the top of the valve body.
    Last edited by kurt s; 09-06-2011 at 06:14 PM.

  11. #11
    Join Date
    Jun 2011
    Location
    Australia
    Age
    44
    Posts
    336
    Rep Power
    21

    Re: Bad TXV ? or solenoid valve?

    Not all power heads are replaceable. If they are replaceable they are usually screwed on and you will see the flats for getting your spanners on, yours probably a sealed unit. Thanks for posting the outcome, always good to find out end result!