    Ltd



    Dear all,,, can any one help me out with the proper LTD ( leaving temp. Difference) for an air cooled water chiller.
    that means the right difference between the water temp. leaving the evaporator and the gas temp leaving the evaporator.
    As I recall back in the 80's it was around 8 degree C .

    Best regards for all

    Rifi



  2. #2
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Ltd

    As a rule of thumb;

    Water outlet temp = Water inlet temp -5°C
    Evaporation temp = Water outlet temp -5°C
    Delta T Total = Water inlet temp - Evaporation temp = 10°C
    The difference between genius and stupidity is that genius has its limits.

    Marc