    Ammonia system



    Dear friends,

    I have to repair an facility that serves the freezing tunnels and storage of frozen products.
    In facts the plant is DX ammonia system which doesn't work properly.

    So, the frozen product ( -20C room temperature) is works properly when the freezing tunnels is off. The tunnels do not reach freezing temperature, even when frozen deposits are stopped.

    So I am thinking about to keep the circuit (DX) for the frozen product store and to mount an separatelly liquid separator pumps and ammonia pumped air coolers for freezing tunnels.


    In fact to use the same compressors and evaporating condenser. But after the liquid receiver to split in one DX circuit and another one for ammonia pumped. For return circuit to join again the two circuits before the suction of compressors.

    Do you think is it possible something like this?
    Will working?

    Thanks for your help.



  2. #2
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Ammonia system

    Are you sure that you have DX coils? Usually, people use TEVs and DX coils for high temp. evaporators.
    To solve the problem, you should find out the reason of this problem. If evaporators, suction line, compressor capacity are under sized, liquid pump will not help.

  3. #3
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Ammonia system

    Herman,

    What's the problem of the plant?
    To make progress is never good enough, I want to do better and better and better

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system

    Hi, herman

    Quote Originally Posted by herman View Post
    Dear friends,

    I have to repair an facility that serves the freezing tunnels and storage of frozen products.
    In facts the plant is DX ammonia system which doesn't work properly.

    So, the frozen product ( -20C room temperature) is works properly when the freezing tunnels is off. The tunnels do not reach freezing temperature, even when frozen deposits are stopped.

    So I am thinking about to keep the circuit (DX) for the frozen product store and to mount an separatelly liquid separator pumps and ammonia pumped air coolers for freezing tunnels.


    In fact to use the same compressors and evaporating condenser. But after the liquid receiver to split in one DX circuit and another one for ammonia pumped. For return circuit to join again the two circuits before the suction of compressors.

    Do you think is it possible something like this?
    Will working?

    Thanks for your help.
    First I have only a few questions, because something is not clear to me...

    A1. How old is your plant? Probably very old..

    A2. The problem you described are from the day one or jump out by the time? Probably from day one ....

    B. What you can tell us about (please, give us some figures):

    1.Capacity of evaporator in cold room/s-freezing storage/s at -20*C
    2.Capacity of freezing tunnels
    3.Capacity of compressor/s at -40*C/35*C (type and size of electrical motor)

    This will put some more light on your plant and hopefully give us chance how to help you.


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    Join Date
    Oct 2006
    Location
    Romania
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Ammonia system

    Quote Originally Posted by Josip View Post
    Hi, herman



    First I have only a few questions, because something is not clear to me...

    A1. How old is your plant? Probably very old..

    A2. The problem you described are from the day one or jump out by the time? Probably from day one ....

    B. What you can tell us about (please, give us some figures):

    1.Capacity of evaporator in cold room/s-freezing storage/s at -20*C
    2.Capacity of freezing tunnels
    3.Capacity of compressor/s at -40*C/35*C (type and size of electrical motor)

    This will put some more light on your plant and hopefully give us chance how to help you.


    Best regards, Josip

    Hallo,

    here are the answers to your questions:

    A1. It's a new one plant; 1 year old

    A2. The problems apperared from the first day

    B 1. 60 kW storing rooms ( -20C)

    B2. 65 kW freezing tunnels ( -30C)

    B3. I don't know the cooling capacity. The compressors 2 pcs, Mycom 200 VLD H; electric motor 200 kW ( Leroy Sommer PLS 315)

    Thank you for your help!

  6. #6
    Join Date
    Oct 2006
    Location
    Romania
    Age
    52
    Posts
    13
    Rep Power
    0

    Re: Ammonia system

    Quote Originally Posted by Sandro Baptista View Post
    Herman,

    What's the problem of the plant?

    Here is the problems:

    So, the frozen product ( -20C room temperature) is works properly when the freezing tunnels is off. The tunnels do not reach freezing temperature, even when frozen deposits are stopped.

    So I am thinking about to keep the circuit (DX) for the frozen product store and to mount an separatelly liquid separator pumps and ammonia pumped air coolers for freezing tunnels.

  7. #7
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Ammonia system

    Quote Originally Posted by herman View Post
    Here is the problems:

    So, the frozen product ( -20C room temperature) is works properly when the freezing tunnels is off. The tunnels do not reach freezing temperature, even when frozen deposits are stopped.

    So I am thinking about to keep the circuit (DX) for the frozen product store and to mount an separatelly liquid separator pumps and ammonia pumped air coolers for freezing tunnels.
    What you mean with frozen deposits are stopped? When the tunnel is empty what is the lower temperature you can reach?

    What's the suction pressure of the comps and its set point. What's happening to the suction pressure when all is working. The cold store share with the tunnels the same compressors, as far I understood, right?
    To make progress is never good enough, I want to do better and better and better

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ammonia system

    What are the operating pressures at the compressor? Have the commissioning start up socks been removed from compressor suction strainer?
    The mycom 200VLD-H should eat the load, at -35/+35 'C = 250 Kw duty.
    Sounds like system loses in pipework maybe something to start with. Liquid overfeed coils are purpose designed, so converstion from DX to flooded is not straight forward.

  9. #9
    Join Date
    Jan 2008
    Location
    West Coast British Columbia
    Age
    51
    Posts
    106
    Rep Power
    17

    Re: Ammonia system

    SINGLE STAGE SCREW COMPRESSOR : 14.0 MYCOMW 14.0ep
    DATE : 05-17-2011
    MODEL : N200VL*-H
    REFRIGERANT : AMMONIA
    RECOMMENDED PORT : H
    BOOSTER : False
    COMPRESSION RATIO : [-] 14.5

    CAPACITY : [kW] 304.4
    CAPACITY : [TR] 86.6
    ABSORBED POWER : [kW] 181.3

    DRIVE SHAFT SPEED : [rpm] 3550
    COMPRESSOR SPEED : [rpm] 3550
    INDICATOR POSITION : [%] 100
    CONDENSING TEMP. : [degC] 35.0
    EVAPORATIVE TEMP. : [degC] -35.0
    SUCTION SUPERHEAT : [degC] 3.00
    LIQUID SUBCOOLING : [degC] 5.00
    SUCTION TEMP. : [degC] -32.0
    OIL SUPPLY TEMP. : [degC] 50.0
    SUCTION PRESS. : [MPaA] 0.093
    DISCHARGE PRESS. : [MPaA] 1.35
    OIL SUPPLY PRESS. : [MPaA] 1.54
    SUCTION PRES. DROP : [MPaA] 0.000
    DISCHARGE PRES. DROP : [MPaA] 0.000

    SWEPT VOLUME : [m3/h] 1460
    LOAD(VOL. FLOW RATE) : [%] 100
    DISCHARGE TEMP. : [degC] 85.5
    REFRIG. FLOW RATE SUC. : [m3/h] 1260
    REFRIG. FLOW RATE DIS. : [m3/h] 127
    REFRIG. FLOW RATE SUC. : [kg/h] 1023
    REFRIG. FLOW RATE DIS. : [kg/h] 1023
    INJECT. OIL FLOW RATE : [L/min] 58.4
    LUB. OIL FLOW RATE : [L/min] 54.6
    F.SIDE OIL FLOW RATE : [L/min] 9.47
    *TOTAL* OIL FLOW RATE : [L/min] 122
    OIL HEAT REJECTION : [kW] 122.7
    OIL SPEC HT : [J/kgK] 1930
    OIL DENSITY : [kg/m3] 880

    COP : [-] 1.68

    --- SUPER HEAT is NOT counted in refrigeration capacity ---

    --- WITH WATER COOLED OIL COOLER ---

    --- Refrigeration oil is not soluble with refrigerant (mineral oil) ---
    --- When choosing the motor set a safety factor of more than 10% for the brake power ---

    plenty of kW's for cooling.

    If it was the suction sock the system would be going down on low suction but the liquid would be hotter than suction pressure.
    Refrigeration is not just cool, it is my life.

  10. #10
    Join Date
    Nov 2004
    Location
    China
    Posts
    176
    Rep Power
    20

    Re: Ammonia system

    Low temperature Dx ammonia systems can be a nightmare. Sounds like some commercial ***** engineer was let loose here. Get rid of all of the expansion valves and install a proper pumped ammonia system. Or bring a bed to the plant 'cause that's where you'll be living.

  11. #11
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system

    Hi, herman

    Quote Originally Posted by herman View Post
    Hallo,

    here are the answers to your questions:

    A1. It's a new one plant; 1 year old

    A2. The problems apperared from the first day

    B 1. 60 kW storing rooms ( -20C)

    B2. 65 kW freezing tunnels ( -30C)

    B3. I don't know the cooling capacity. The compressors 2 pcs, Mycom 200 VLD H; electric motor 200 kW ( Leroy Sommer PLS 315)

    Thank you for your help!
    Seems you have enough cooling capacity within compressors - I prefer tunnel evaporating temperature to be -45*C or max -40*C freezing must be very fast to protect the goods (-35*C ET we use for ice cream cold room to keep the room at -26*C - safety margin for handling), but even at evaporating temperature of -45*C your compressor will give more capacity then you actually need....

    Hope that you have suction pipe size min of DN 150mm/6" i.e. common suction pipe for parallel work of cold storage room and tunnel ...

    One more question ... can you reach freezing temperature when your tunnel is empty or 25% i.e. 50% full?

    Something must be wrong with DX system for freezing tunnel ... I agree with charlie n to revamp that one to pump system ....



    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  12. #12
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Ammonia system

    Hi Iceman_ 4000.
    I quoted duty at 50 Hz. Do not know what power supply is in Romania

  13. #13
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Ammonia system

    Quote Originally Posted by Magoo View Post
    Hi Iceman_ 4000.
    I quoted duty at 50 Hz. Do not know what power supply is in Romania
    If you see the speed motor he considered 3.550 rpm (60 Hz)
    To make progress is never good enough, I want to do better and better and better

  14. #14
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Ammonia system

    Hi, IceMan_4000



    Quote Originally Posted by IceMan_4000 View Post
    SINGLE STAGE SCREW COMPRESSOR : 14.0 MYCOMW 14.0ep
    DATE : 05-17-2011
    MODEL : N200VL*-H
    REFRIGERANT : AMMONIA
    RECOMMENDED PORT : H
    BOOSTER : False
    COMPRESSION RATIO : [-] 14.5

    CAPACITY : [kW] 304.4
    CAPACITY : [TR] 86.6
    ABSORBED POWER : [kW] 181.3

    DRIVE SHAFT SPEED : [rpm] 3550
    COMPRESSOR SPEED : [rpm] 3550
    INDICATOR POSITION : [%] 100
    CONDENSING TEMP. : [degC] 35.0
    EVAPORATIVE TEMP. : [degC] -35.0
    SUCTION SUPERHEAT : [degC] 3.00
    LIQUID SUBCOOLING : [degC] 5.00
    SUCTION TEMP. : [degC] -32.0
    OIL SUPPLY TEMP. : [degC] 50.0
    SUCTION PRESS. : [MPaA] 0.093
    DISCHARGE PRESS. : [MPaA] 1.35
    OIL SUPPLY PRESS. : [MPaA] 1.54
    SUCTION PRES. DROP : [MPaA] 0.000
    DISCHARGE PRES. DROP : [MPaA] 0.000



    --- SUPER HEAT is NOT counted in refrigeration capacity ---

    --- WITH WATER COOLED OIL COOLER ---

    --- Refrigeration oil is not soluble with refrigerant (mineral oil) ---
    --- When choosing the motor set a safety factor of more than 10% for the brake power ---

    plenty of kW's for cooling.

    If it was the suction sock the system would be going down on low suction but the liquid would be hotter than suction pressure.
    In Romania they use 50 Hz i.e. capacity is 20% lower, but still enough around 240kW....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  15. #15
    Join Date
    Jan 2008
    Location
    West Coast British Columbia
    Age
    51
    Posts
    106
    Rep Power
    17

    Re: Ammonia system

    Ops sorry guys totally missed the 50hz

    Thanks for the correction Josip

    SINGLE STAGE SCREW COMPRESSOR : 2011 MYCOMW 2011ep
    DATE : 05-18-2011
    MODEL : N200VL*-H
    REFRIGERANT : AMMONIA
    RECOMMENDED PORT : H
    BOOSTER : False
    COMPRESSION RATIO : [-] 14.5

    CAPACITY : [kW] 243.5
    CAPACITY : [TR] 69.2
    ABSORBED POWER : [kW] 159.6

    DRIVE SHAFT SPEED : [rpm] 2950
    COMPRESSOR SPEED : [rpm] 2950
    INDICATOR POSITION : [%] 100
    CONDENSING TEMP. : [degC] 35.0
    EVAPORATIVE TEMP. : [degC] -35.0
    SUCTION SUPERHEAT : [degC] 0.00
    LIQUID SUBCOOLING : [degC] 5.00
    SUCTION TEMP. : [degC] -35.0
    OIL SUPPLY TEMP. : [degC] 50.0
    SUCTION PRESS. : [MPaA] 0.093
    DISCHARGE PRESS. : [MPaA] 1.35
    OIL SUPPLY PRESS. : [MPaA] 1.55
    SUCTION PRES. DROP : [MPaA] 0.000
    DISCHARGE PRES. DROP : [MPaA] 0.000

    SWEPT VOLUME : [m3/h] 1210
    LOAD(VOL. FLOW RATE) : [%] 100
    DISCHARGE TEMP. : [degC] 82.4
    REFRIG. FLOW RATE SUC. : [m3/h] 994
    REFRIG. FLOW RATE DIS. : [m3/h] 96.4
    REFRIG. FLOW RATE SUC. : [kg/h] 816.8
    REFRIG. FLOW RATE DIS. : [kg/h] 816.8
    INJECT. OIL FLOW RATE : [L/min] 58.4
    LUB. OIL FLOW RATE : [L/min] 54.6
    F.SIDE OIL FLOW RATE : [L/min] 9.48
    *TOTAL* OIL FLOW RATE : [L/min] 123
    OIL HEAT REJECTION : [kW] 112.3
    OIL SPEC HT : [J/kgK] 1930
    OIL DENSITY : [kg/m3] 880

    COP : [-] 1.53

    --- SUPER HEAT is NOT counted in refrigeration capacity ---

    --- WITH WATER COOLED OIL COOLER ---

    --- Refrigeration oil is not soluble with refrigerant (mineral oil) ---
    --- When choosing the motor set a safety factor of more than 10% for the brake power ---
    Refrigeration is not just cool, it is my life.

  16. #16
    Join Date
    Jan 2008
    Location
    West Coast British Columbia
    Age
    51
    Posts
    106
    Rep Power
    17

    Re: Ammonia system

    -45 capacity

    SINGLE STAGE SCREW COMPRESSOR : 2011 MYCOMW 2011ep
    DATE : 05-18-2011
    MODEL : N200VL*-H
    REFRIGERANT : AMMONIA
    RECOMMENDED PORT : H
    BOOSTER : False
    COMPRESSION RATIO : [-] 24.8

    CAPACITY : [kW] 136.5
    CAPACITY : [TR] 38.8
    ABSORBED POWER : [kW] 140.4

    DRIVE SHAFT SPEED : [rpm] 2950
    COMPRESSOR SPEED : [rpm] 2950
    INDICATOR POSITION : [%] 100
    CONDENSING TEMP. : [degC] 35.0
    EVAPORATIVE TEMP. : [degC] -45.0
    SUCTION SUPERHEAT : [degC] 0.00
    LIQUID SUBCOOLING : [degC] 5.00
    SUCTION TEMP. : [degC] -45.0
    OIL SUPPLY TEMP. : [degC] 50.0
    SUCTION PRESS. : [MPaA] 0.054
    DISCHARGE PRESS. : [MPaA] 1.35
    OIL SUPPLY PRESS. : [MPaA] 1.55
    SUCTION PRES. DROP : [MPaA] 0.000
    DISCHARGE PRES. DROP : [MPaA] 0.000

    SWEPT VOLUME : [m3/h] 1210
    LOAD(VOL. FLOW RATE) : [%] 100
    DISCHARGE TEMP. : [degC] 81.6
    REFRIG. FLOW RATE SUC. : [m3/h] 933
    REFRIG. FLOW RATE DIS. : [m3/h] 54.7
    REFRIG. FLOW RATE SUC. : [kg/h] 464.6
    REFRIG. FLOW RATE DIS. : [kg/h] 464.6
    INJECT. OIL FLOW RATE : [L/min] 60.2
    LUB. OIL FLOW RATE : [L/min] 55.1
    F.SIDE OIL FLOW RATE : [L/min] 9.58
    *TOTAL* OIL FLOW RATE : [L/min] 125
    OIL HEAT REJECTION : [kW] 111.7
    OIL SPEC HT : [J/kgK] 1930
    OIL DENSITY : [kg/m3] 880

    COP : [-] 0.972

    --- SUPER HEAT is NOT counted in refrigeration capacity ---

    --- WITH WATER COOLED OIL COOLER ---

    --- Refrigeration oil is not soluble with refrigerant (mineral oil) ---
    --- When choosing the motor set a safety factor of more than 10% for the brake power ---
    Refrigeration is not just cool, it is my life.

  17. #17
    Join Date
    Mar 2004
    Location
    Peckham,London
    Age
    38
    Posts
    24
    Rep Power
    0

    Re: Ammonia system

    looks like compressor has enough capacity!

    DX??

    you should go flooded evaps, pumped recirculation with low pressure receiver. Pipe work length will have an effect on DX refrig. pumped recirc with low pressure receiver will over come this.
    fridge

  18. #18
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Ammonia system

    DX is basically a NO-NO for anything below about 10 degF for ammonia. There is too may problems associated with proper circuiting and and feeding the coil circuits. To be quiet blunt, anyone that would install a DX ammonia freezer like you described has to be a total idiot.

    You can probably redo the feed headers on the coils and add a gravity or liquid recirculation system and make the coils work.