    Compressor not starting Fujita split system



    Hi fellas, I recently removed/replaced an old Fujita split and decided to take the old split home for some fault finding. Its a Fujita AS-H12A4/HS, fixed speed compressor about 6 years old now (I'm aware Fujita is not the best quality). As I mentioned in another thread my licence does not allow me to fix and repair but I have this one sitting at my place and would like to learn more about service/fault finding etc split systems. I reclaimed approx 700g of R22 upon removal (spec plate states quantity of unit to be 720g) so ofcourse that rules out a refrigerant issue. Basically what was happening on both heating and cooling attempts the condensor fan will start up as well as evaporator fan (only on cooling obviously) but the compressor will not run. I could hear the compressor try to start, it would vibrate slightly for about 1-2 seconds then a relay would click and compressor would "stop". This would happen every say 10 seconds over and over. Any ideas what I should start testing first, capacitor etc and what the problem likely may be? Thanks in advance



  2. #2
    Join Date
    Apr 2010
    Location
    Australia
    Posts
    31
    Rep Power
    0

    Re: Compressor not starting Fujita split system

    Ok done a few tests (may need to be corrected on), first with the compressor. Put a megger on the windings and got;
    Went from Start lead to common lead and got approx 2.7 ohm
    Went from Run lead to common lead and got approx 1.75 ohm
    Went from Run lead to Start lead and got approx 4.45 ohm which adds up
    I have never tested capacitors but had a quick look, it seems to be a 35microF/450VAC capacitor. There were a total of 4 terminals, seperated into 2 sets. On one set came the wire from the supply, and also a red wire that goes to the Run terminal of compressor. On the second set there was a yellow wire that goes to the Start terminal on compressor. The other terminal in this set was not used. I tested the capacitor disconnected and figured I'd go from each terminal that connects both Run and Start terminals. Ended up getting 1.675microF on my tester, which means? I got the same figure going from the terminal Run terminal to the unused terminal but nothing between the Run terminal and the supply terminal. Not sure what I should be getting and how readings are meant to be interpreted? I connected everything back up (including pipes and interconnect etc) and decided to clamp test each wire. I clamped the supply wire as well as each Run and Start wire from the cap to the compressor. Supply and Run (each red wire seperatley) reached approx 35 Amps each time the compressor tried to start for that 1-2 seconds, however did not get any reading on the Start wire (yellow wire) at all which seems odd to me, I thought It would be the other way around? Any way if someone can decipher this that would be great
    Last edited by alan_man; 05-05-2011 at 06:01 AM.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Compressor not starting Fujita split system

    Try a new capacitor, old one sounds like its failed, they often have two pairs of terminals, so to ins and to outs in effect. Some capacitors also include the fan cap in the same can, this would be something like a 35uf/5uf for example. This could have three or six terminals depending on design.

    Jon
    Mostly found in Oxfordshire, UK :)

  4. #4
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Compressor not starting Fujita split system

    Could you check you are getting the correct voltage at the compressor windings

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor not starting Fujita split system

    I know that this isn't for your compressor but is a useful set of guidelines for compressor install and wiring etc...

    http://hvac.amickracing.com/Compress...structions.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Apr 2010
    Location
    Australia
    Posts
    31
    Rep Power
    0

    Re: Compressor not starting Fujita split system

    Bingo, changed the capacitor and the unit runs good as gold now. thanks for the replies and that pdf was a good read

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Compressor not starting Fujita split system

    Good news and thanks for the update.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  8. #8
    Join Date
    Apr 2005
    Location
    Manchester England
    Age
    43
    Posts
    332
    Rep Power
    20

    Re: Compressor not starting Fujita split system

    whats the plan for the now working system?

  9. #9
    Join Date
    Apr 2010
    Location
    Australia
    Posts
    31
    Rep Power
    0

    Re: Compressor not starting Fujita split system

    Quote Originally Posted by moondawn View Post
    whats the plan for the now working system?
    Well the unit has been evacuated, recharged and pumped down. A friends wants to install it in a granny flat he has at his house so I will probably pass it off to him. If you were in Australia and were interested we could have worked something out

  10. #10
    Join Date
    Jan 2003
    Location
    Crewe, United Kingdom
    Age
    58
    Posts
    723
    Rep Power
    22

    Re: Compressor not starting Fujita split system

    That's going to be one hell of a callout charge Alf, the OP is in Austrailia...... Can you smell SPAM cooking?
    Karl

  11. #11
    Join Date
    Jan 2012
    Location
    Australia
    Posts
    1
    Rep Power
    0

    Re: Compressor not starting Fujita split system

    I just joined up to say - Thank you Thank you Thank you!!

    You guys just saved me a fortune!

    I had the exact same problem on a 38 degree day and after reading this thread I figured it was worth it to change the capacitor. And it worked!

    Thank you guys! Saved me a lot of money and a lot of work. Woohoo!