Results 1 to 9 of 9
Thread: capacity
    Oct 2009
    merida mexico
    54
    282
    15
    capacity
    question:
    I have a machine Frick RXF-85 OF 170 TR ammonia that I installed capacity condenser, I install a plate heat exchanger.
    thanks
    Jul 2008
    Houston Tx
    42
    Re: capacity
    Are you needing help or just letting us know?? I work with approx. 15 RXF85's a month if you have a question please ask I would love to help you..
    Oct 2009
    merida mexico
    54
    282
    15
    Re: capacity
    I have doubts as to the heat exchanger. what capacity should I install? conditions are temp. water 30 ° c and 37 ° c output
    Auckland
    74
    3,357
    38
    Re: capacity
    With those water temps you will be having high discharge pressure problems. The problem would seem to be with the cooling tower, undersized or overloaded. Maybe the compressor is loading too quick during pull down.
    Oct 2009
    merida mexico
    54
    282
    15
    Re: capacity
    magoo:
    what would your recommendation, we have an outside temperature of 42 ° c
    Jan 2006
    Croatia
    68
    2,261
    31
    Re: capacity
    Hi, serviceman
    Quote Originally Posted by serviceman View Post
    magoo:
    and relative humidity very low ....
    .... then your wet bulb temperature will be around 25-26*C or lower ... with good cooling tower your can have condensing temperature lower or up to 35*C what is still good ... very good ... OK not the best
    assuming you are in hot and dry area of Mexico ....
    check your cooling tower as per Magoo's suggestion....
    Best regards, Josip
    Oct 2009
    merida mexico
    54
    282
    15
    Re: capacity
    josip
    area of mexico 80% rh
    Auckland
    74
    3,357
    38
    Re: capacity
    With 42 'C ambient and 80% RH. That is a problem. Can you lower the rise across condenser from 7'K to 5.0> 5.5'K by increasing water flow rate, that will drop the SDT slightly. If the make up water temp is lower again try over filling basin.
    Jul 2008
    Houston Tx
    42
    Re: capacity
    Im in Houston TX and we have same humidity and close to same outside temps as the others said above I would look at the condenser but I do have a cpl other questions. What does your suction psi run and is this compressor a econamized unit, also I would like to ask what type of plant it is..