    capacity



    question:

    I have a machine Frick RXF-85 OF 170 TR ammonia that I installed capacity condenser, I install a plate heat exchanger.

    thanks



  2. #2
    Join Date
    Jul 2008
    Location
    Houston Tx
    Posts
    42
    Rep Power
    0

    Re: capacity

    Are you needing help or just letting us know?? I work with approx. 15 RXF85's a month if you have a question please ask I would love to help you..

  3. #3
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: capacity

    I have doubts as to the heat exchanger. what capacity should I install? conditions are temp. water 30 ° c and 37 ° c output

  4. #4
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: capacity

    With those water temps you will be having high discharge pressure problems. The problem would seem to be with the cooling tower, undersized or overloaded. Maybe the compressor is loading too quick during pull down.

  5. #5
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: capacity

    magoo:

    what would your recommendation, we have an outside temperature of 42 ° c

  6. #6
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: capacity

    Hi, serviceman

    Quote Originally Posted by serviceman View Post
    magoo:

    what would your recommendation, we have an outside temperature of 42 ° c

    and relative humidity very low ....

    .... then your wet bulb temperature will be around 25-26*C or lower ... with good cooling tower your can have condensing temperature lower or up to 35*C what is still good ... very good ... OK not the best

    assuming you are in hot and dry area of Mexico ....


    check your cooling tower as per Magoo's suggestion....



    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  7. #7
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: capacity

    josip

    area of mexico 80% rh

  8. #8
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: capacity

    With 42 'C ambient and 80% RH. That is a problem. Can you lower the rise across condenser from 7'K to 5.0> 5.5'K by increasing water flow rate, that will drop the SDT slightly. If the make up water temp is lower again try over filling basin.

  9. #9
    Join Date
    Jul 2008
    Location
    Houston Tx
    Posts
    42
    Rep Power
    0

    Re: capacity

    Im in Houston TX and we have same humidity and close to same outside temps as the others said above I would look at the condenser but I do have a cpl other questions. What does your suction psi run and is this compressor a econamized unit, also I would like to ask what type of plant it is..