    Mar 2010
    Bangladesh
    34
    151
    9
    AHU total load calculation?
    Room Size: 168 m3, Air change/Hr: 20, CFM: 1975, Outside Temp:104 F, Room Required temp: 71 F, Outside RH: 85%, Expected RH: 22%, system required 20 % fresh air and 80 % return air.
    So, Sensible Heat: 1.085X1975X(104-71)/12000 = 5.87 Ton
    & Latent Heat: 4.840X1975X (139 - 31.43)/12000 = 86 Ton,
    if I overlook other heating load, then total load = 91.87 Ton, but I don't think so, its too much for 168 m3 room, what was my problem with the calculation? Please help?
    Auckland
    68
    3,362
    32
    Re: AHU total load calculation?
    Try electrcal loading from lights, computers, fans, and people loadings. Heat gain from solar effect on windows. heat gain from structure loads, ceilings walls and floors.
    Split Croatia
    52
    6,108
    31
    Your problem is that you are probably calculating whole air as fresh air, not mixed!
    You need to handle only 20% of total air flow as fresh air.
    Mar 2010
    Bangladesh
    34
    151
    9
    Thanks to you, you always help me lot.
    Can you please provide me the software or the source of the software or how can I calculate it my self?
    Waiting for your kind replay.
    Split Croatia
    52
    6,108
    31
    Windows Psychrometrics Calculator 28.00
    http://www.marcobrien.org.uk/
    Mar 2010
    Bangladesh
    34
    151
    9
    ok I will do it.................
    Mar 2010
    Bangladesh
    34
    151
    9
    Some problem with the calculation......
    1. Supply air dry and wet bulb temperature is not correct our expected temperature 22 Deg C and 22% RH
    Split Croatia
    52
    6,108
    31
    That is exactly what I entered as return air.
    Return air is actual state of air in room.
    Supply air is mixing with air alredy in room.
    Check your home air-conditioner suply air and room air.
    Mar 2010
    Bangladesh
    34
    151
    9
    But this is not a total summary. Where is my 20% fresh air load and at the starting time room temperature and humidity are same as outside so how can I summaries total scenario?Its a pharmaceuticals plant......
    My point is
    (Room Size: 168 m3, Air change/Hr: 20, CFM: 1975, Outside Temp:104 F, Room Required temp: 71 F, Outside RH: 85%, Expected Room RH: 22%, system required 20 % fresh air and 80 % return air.) if I want to calculate from the beginning what will be the steps?
    1. Sensible Heat: cfmX1.085X (Tout-Tin)/12000 = (0.00 Ton)
    2. Latent Heat: cfmX0.69143X(G1-G2)/12000 = (0.00 Ton)
    Then add lighting, man, machine, sunlight, .........etc load, but problem is at normal condition and initial condition load is not safe so how can I summarized total thing that can help me to predict system total load and buy a AHU.
    Split Croatia
    52
    6,108
    31
    Quote Originally Posted by Bashir01219 View Post
    20% fresh air is in the calculation.
    What is not in calculation:
    -Latent load from people
    -Heat gain from the supply air fan
    -Heat gain from the return air fan
    -Heat gain from supply air ductwork portion in unconditioned space
    - Heat gain from return air ductwork in unconditioned space
    - Infiltration (sensible & latent) if any
    - Heat gain from lights
    - Heat gain from plant equipment
    - Heat gain from walls, floors, ceilings and windows
    etc...
    Also, you need to establish what is required time frame to lower your temperature from starting conditions.
    Than , you could calculate aditional cappacity needed for that task.
    Mar 2010
    Bangladesh
    34
    151
    9
    In the chart Mixed Air Return, for Supply Air, you take DB:12.3, WB: 11.3, RH:95 why? Is it not what for the room design? RH: 22, Temp.: 22 Deg C.