    Re: Suction Pressure



    Q Both coolers have the same set point temp of 35F SH 30 and SC 15 at design temp. My question is this. The head pressure for both are 265 psi but on the low side, the 3 hp has 72 psi and the 5hp has 50 psi. Both were at design temp when sc and sh were taken.
    At 35°F set temperature, 72 psig (30°F evaporation saturation temperature) does not seam possible unless compressor did not worked at time of measurment.
    Check your measurments again and take SH reading (both pressure and temperature) at evaporator outlet.
    Last edited by nike123; 30-04-2011 at 07:32 AM.



  2. #2
    Join Date
    Jun 2010
    Location
    USA
    Posts
    89
    Rep Power
    14

    Re: Suction Pressure

    Quote Originally Posted by nike123 View Post
    At 35°F set temperature, 72 psig (30°F evaporation saturation temperature) does not seam possible unless compressor did not worked at time of measurment.
    Check your measurments again and take SH reading (both pressure and temperature) at evaporator outlet.
    That could be the case nike123. The system got knocked out by power failure and took several attempts to get the compressor started. Made terrible noises at start up. Once it finally started, it tripped on head pressure saftey a few times. then after a couple of hours once it was running i took sc and sh measurements. So does that mean this compressor is going into failure ? will valving off and seeing if it will pull a vacuum give the answer ?

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Suction Pressure

    Quote Originally Posted by jakb21599 View Post
    That could be the case nike123. The system got knocked out by power failure and took several attempts to get the compressor started. Made terrible noises at start up. Once it finally started, it tripped on head pressure saftey a few times. then after a couple of hours once it was running i took sc and sh measurements. So does that mean this compressor is going into failure ? will valving off and seeing if it will pull a vacuum give the answer ?
    Yes, compressor should pull to about 0,3 Bara (absolute) very quickly and then, in 2 min period, it should not get to 1 Bara.
    Last edited by nike123; 02-05-2011 at 08:31 AM.