Results 1 to 10 of 10
  1. #1
    Join Date
    May 2005
    Location
    SPORE
    Age
    53
    Posts
    20
    Rep Power
    0

    Problem:water dripping from a/c unit



    hi, can anyone tell me y water start dripping out from fan coil unit when there is shortage in gas pressure ??



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Problem:water dripping from a/c unit

    When there is shortage of refrigerant, evaporating temp is dropping and so is the coil surface.
    In many cases, the result will be iced coil.

    Comprende?

    Chemi

  3. #3
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: Problem:water dripping from a/c unit

    Hi.ong

    Refrigerant shortage can cause uneven ice to form on the evaparator coil (rather than sweating).
    The ice either defrosts partially and often redirects droplets over the driptray out of the airhandler.

    Kind regards. Mark

  4. #4
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: Problem:water dripping from a/c unit

    I was told this by Tech support of a well known brand.

    when the unit is slightly short of gas the last few runs of the coil dont sweat properly.

    Any runs above this that are sweating properly rely on moisture forming on the runs below runs below. The condensate runs down the face of the coil like a wick effect into the drain.

    In the case of slightly short of gas the condensate drops straight onto the indoor unit fan and spits out with the supply air.

    I have seen this on a unit that on first glance appears to be charged properly. But upon further investigation it was only slightly short.

    Also have seen they same thing when one pipe of a distributor was blocked on indoor unit and was not allowing gas to flow on some of the runs.

    Mainly applies to high wall splits.

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem:water dripping from a/c unit

    Chemi said it all.
    With A/C you want the coil to remain above freezing so that the coil only sweats. If the system is short of charge then the coil can become sub-zero and frost can form causing too much condensate to overflow when the system cycles off.

  6. #6
    Join Date
    Jun 2003
    Location
    northampton
    Posts
    20
    Rep Power
    0

    Smile Re: Problem:water dripping from a/c unit

    buy a bigger bucket !!!!!!!!!!

    Get this all the time with older imi units coils get a bit tired water everywhere find the leak and top it up !!!
    Leak in the fridge circuit

    also found sometimes that the ac split is not level in the ceiling even if the sytem is lo on gas will drain in to one point and flow over the top

    good luck
    Last edited by phil; 29-09-2005 at 07:46 PM.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem:water dripping from a/c unit

    coils get a bit tired
    Hi Phil
    Never heard of this before - is it a common saying down your way? what does it mean exactly?
    also found sometimes that the ac split is not level in the ceiling even if the sytem is lo on gas will drain in to one point and flow over the top
    Surely, this problem would show up from day one? Do you mean that they operate correctly for some time and then slope on the wall or in the ceiling causing the condensate to spill?
    Do you check your installs to verify that the condensate drains corectly?

  8. #8
    Join Date
    Jun 2003
    Location
    northampton
    Posts
    20
    Rep Power
    0

    Re: Problem:water dripping from a/c unit

    us yokels in the east midlands hav this funny way of talkin !!!

    it means its not quite knackered but soon will be if it left any longer

    in most case the coils are beginning to corode away grey falking and crumbling see a lot of this on condenser units by the east anglia coast where the salt air attacks the aluminuim

    copper pipework also suffers by pitting or liitle holes developling again caused by corrosion this can lead to refrigerant slowly leaking away. had the same some times on williams cabinets using r134a ie the catering benches fridge with the fans in the top

    phil

  9. #9
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Problem:water dripping from a/c unit

    Hi Phil

    I now understand
    By the way, Nottingham is in the East Midlands

  10. #10
    Join Date
    Jun 2003
    Location
    northampton
    Posts
    20
    Rep Power
    0

    Re: Problem:water dripping from a/c unit

    northampton should adopt a new song we are in the middle of nowhere no manufacturing as such now only logistics conpanies

    i very rarely work in northants now mostly east anglia and lovely london not the city thank god !!!!!!!!!!!!

Similar Threads

  1. Daikin a/c units.
    By rick in forum Air Conditioning
    Replies: 59
    Last Post: 18-02-2008, 09:22 PM
  2. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM
  3. M I T S U S H I T A ac unit with no condensing unit
    By Chinua in forum Air Conditioning
    Replies: 2
    Last Post: 28-07-2006, 06:54 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •