Thread: Sight Glass,
    Apr 2001
    2,099
    27
    Sight Glass,
    We were "told" that a full sight glass devoid of bubbles is indicative of a full or charged system. How true is this? Recently I have had an evaporator which iced over very nicely, but the sight glass still showed up half full and bubbling. This was a new installation, mind you, a 1.5 hp hermetic compressor with an externally equalised valve, Danfoss with orifice number 2. Room temperature +1 Celcius and running on R404. Is the orifice perhaps too big , Number 2, or should it have been a number 1. I note in a previous thread that the drier position sgould always point downwards from the receiver.
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.
    St. Louis, MO
    509
    Of course, we are considering a system using a TEV. Systems using a cap tube or restrictor as a metering device shouldn't have a sight glass installed...
    A #2 orifice on a 1-1/2 hp R-404A compressor seems appropriate, though additional information would be necessary, i.e., evaporator temperature, condensing temperature, subcooling, and compressor capacity, to determine if it is the optimal orifice size.
    Also, one can have a situation where you have a properly sized TEV, excessive flashing in the liquid line, the TEV adjustment turned all the way out, and the system appears to be operating normally. The problem here, of course, is the TEV isn't doing any modulating, other than simply acting like an orifice.
    A few bubbles in the liquid line now and then aren't going to cause problems. But excessive flash gas in the liquid line is asking for trouble. So, what do we mean by "excessive"? Enough to displace a significant amount of liquid flow thru the TEV.
    Answers like this is what makes servicing refrigeration systems interesting...
    Prof Sporlan
    Apr 2001
    79
    5,071
    35
    I tend to ignore the sightglass. It's misleading. To me it's just a moisture indicator. Instead I monitor subcooling and superheat. I find overcharged systems everywhere I go.
    Apr 2001
    79
    5,071
    35
    I monitor subcooling at the start of the liquid line (receiver outlet). My purpose in doing so is to avoid overcharging the system, which I define as exceeding 15F subcooling. Beyond this limit, liquid is beginning to back up into the condenser, driving up the head pressure.
    On all systems, whether TEV or fixed orifice:
    My primary goal is to flood the evaporator.
    My secondary goal is to cool (but not flood) the compressor.
    My tertiary goal (TEV system) is to provide surplus refrigerant.
    In no case is the subcooling allowed to exceed 15F.
    There are instances where extra subcooling is needed, but there are better ways to acheive this than driving up the head pressure.
    Apr 2001
    79
    5,071
    35
    I don't disagree with any of this, Marc. The balance (or imbalance) between subcooling and superheat, resulting in inability to reach these goals within my limits, indicates mismatched components and/or the exceptions you mentioned.
    Would I raise head pressure to get the system working? Yes. But I would know that I was doing so, and why. And I would recommend alternatives to the customer.
  1. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Last Post: 18-07-2006, 08:16 PM
  2. sight glass
    By daleworne in forum Trouble Shooting
    Last Post: 17-06-2006, 11:43 PM
  3. Sight glass , Flashing ?
    By kfjoe in forum Fundamentals
    Last Post: 14-02-2004, 04:41 AM
  4. Sight Glass Located
    By Abe in forum Trouble Shooting
    Last Post: 22-01-2002, 01:22 AM