    Cascade system -90*C



    hii all,

    iam new in this forum, please give me some advise cause my problem as follow :

    my cascade system using two compressor Danfoss gs26clx for both stage.
    Condensor 1 HP Power, Filter Drier, Double Pipe Hx, Expansion Tank 1 Hp.
    High Stage Refrigerant using R1270 and Low Stage Refrigerant using R1150.
    Freezer Evaporator about 260 Ltr. need temperature -90*C.
    that system already running very well almost 1 week. after that the low stage LP become vaccum zone. and temperature going rise up to the room temperature.

    somebody please help me to solve this problem.

    thanks,
    Regards,



    Edi



  2. #2
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: Cascade system -90*C

    when the system where ok then what was the Ampir of the system. and after the fault what ampirs shows on A meter.
    2nd. what is the pozition of bubbles in sight glass.
    3rd. what is the gauge pressure when system is not working.

  3. #3
    Join Date
    Mar 2010
    Location
    pakistan
    Posts
    44
    Rep Power
    0

    Re: Cascade system -90*C

    tell me the full detal of ur cooling unit.

  4. #4
    Join Date
    Dec 2008
    Location
    USA
    Age
    42
    Posts
    57
    Rep Power
    16

    Re: Cascade system -90*C

    Most likely oil logging.. Use some kind of solvent to flush through the cap tube. To confirm the logging check the evap temperature inlet and outlet ( if its possible).