    Fujitsu Split AC errors



    hi.

    I have a fujitsu split AC. Indoor is an ASYA24LCC & the outdoor is an AOYR24LCL.

    The problem is that the green timer light is showing a fault. Firstly it flashes twice then after a few minutes flashes 3 times. The operation light is off whilst this happens.
    According to the info I do have it says the fault is reverse comms fail on start up and reverse comms fail in use.
    I have no more info on how to remedy this fault.
    I have checked the wiring and all is as it should be. Is it simply a fault with the indoor or outdoor PCB? or is there more to it?
    Btw,I have no manuals on these units.


    Any help much appreciated

    P W.



  2. #2
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Fujitsu Split AC errors

    Try reading this: http://www.refrigeration-engineer.co...read.php?15069
    Make sure the outdoor unit has 240v AC supply to the PCB and out, into the inverter and out 320V DC

  3. #3
    Join Date
    May 2008
    Location
    ENGLAND
    Posts
    61
    Rep Power
    16

    Re: Fujitsu Split AC errors

    Hello PW,

    Does your condensor fan or compressor run at all? Got the same unit and my problem is condensor fan only runs for a few seconds ...no signs of life from compressor either in cool/heat...juice to it and managed to blow a board connected to comp! Would be interested to know if you've had similar problems???

    Thanks,

    Pie Man