    May 2008
    malaysia
    34
    82
    11
    chiller cooling capacity
    hey guy, i m confuse with this.... hopefully can get some explanation...
    - system cooling capacity KW
    - compressor capacity KW
    - expansion valve kw?
    for example if chiller capacity 100KW, what is the relation between compressor, condenser, expansion valve, and evaporator....
    can share some formula & calculation for this?
    thanks...
    Oct 2003
    56
    5,519
    28
    Re: chiller cooling capacity
    100 kW cooling, +/- 3 COP = 33 kW compressor capacity or 25 kW at a COP of 4
    COP is a factor of the working conditions (LP versus HP)
    Expansion valve is 100 kW at a certain evaporation capacity and a certain subcool and a DP over the valve
    There are no formulas nor calculations for this, only manuals/selection tables of the different manufacturers.
    May 2008
    malaysia
    34
    82
    11
    thanks a lot... bro...
    means we can see the system cooling KW from the expansion device... right!!!!
    Oct 2003
    56
    5,519
    28
    Yes and no, you only can make a rough guess because the expansion system can regulate its capacity within a certain margin.
    May 2008
    malaysia
    34
    82
    11
    thanks....