TEV range
Hi sir
VFD compressor frequency form 30 to 90Hz,capacity from 10 to 27kW, i'm not sure if it can match well with thermal expansion valve which need the 30%~100% capacity range . pls help to confirm it.
rgds
LC
-
18-09-2006, 01:49 PM #2
Re: TEV range
There is no effect on expansion valves during modulation. You should select expansion valve at 27KW rating.
-
18-09-2006, 04:51 PM #3
Re: TEV range
Hi LC,
I normally recommend a minimum turn-down capacity of 50% for TXV's. If the full capacity requirement is 27 kW, then the minimum allowable capacity (for good control of the superheat) would be about 13.5 kW.
At 10 kW, you are at about 40% of the valve capacity assuming nothing else changes. The liquid feed pressure may decrease due to the excess condenser surface available at part load though.
An electronic expansion valve may produce better results, but all of my experience is with mechanical TXV's.
-
19-09-2006, 02:20 AM #4
Re: TEV range
Hi, Mr sze.
I agree with Saint. The TXV should fit to the max capacity. During the modulation, TXV could regulate the turn-down rating by the pressure of temperature sensor. As Iceman said, the EXV will enhance the precision of regualtion.
-
19-09-2006, 04:58 AM #5
Re: TEV range
Originally Posted by ernestlin
-
19-09-2006, 08:08 AM #6
Re: TEV range
One should remember 2 things:
- TXV are able to handle more then their nominal capacity. Mostly 20 % more, some valve even 30%. So I don't agree to select the valve on the maximum capacity.
- the capacity of a certain TXV is (almost) linear with the superheat. (large capacity = large superheat; small capacity = small superheat). So if you need a constant (or an as low as possible) superheat over the full capacity range, an electronic expansion valve is the best choice.
-
19-09-2006, 10:05 AM #7
-
19-09-2006, 02:20 PM #8
Re: TEV range
Could you not fit two TEV's one rated at 15kw and one at 28kw and switch between them with a couple of solenoid valves to match compressor speed/capacity? Could solenoid control be tied in to the variable speed control system? An old alfa laval glycol/slush maker i saw on a dairy farm had a load of capillaries run in parallel with a TEV, did'nt switch between them though.
-
20-09-2006, 09:19 AM #9
-
20-09-2006, 03:16 PM #10
Re: TEV range
I wote for 2 TEV.But wich kind of machine is this?
Renato
-
20-09-2006, 08:50 PM #11
Re: TEV range
instead of 1 at 27kw and one at 15kw and solenoides to change between them....
why not just 2 at 15kw and a solenoide to turn one and off ?
(p.s. Lc_shi... wait till someone who knows what there doing posts before you go out buying bits!)
-
21-09-2006, 01:29 AM #12
Re: TEV range
Hi knighty
yeah, totally agree with you
But i prefer to use 27kw and it can cover 15kw capacity point. I'll test it and the fact will have the say.
regards
LCI hear...I forget;I see...I remember;I do...I understand
-
21-09-2006, 05:23 PM #13
Re: TEV range
What i was thinking was that at the point of switching between 15Kw and 27Kw both valves would be sensing the same evaporator pressure and superheat, would the 27Kw valve have shut down to about 15Kw to match the load, and hence cause a seemless transision from the 7.5Kw/15Kw range to the 13.5Kw/27Kw range? Would this work equally going down in capacity? If we had two valves of 15Kw would the second valve be at 15Kw as its brought on line? Giving 30Kw until both valves can adjust? I'm asking not telling, this needs someone brighter than me on it
Cheers Jon
Similar Threads
-
Toshiba Digital Inverter range?
By Slim R410a in forum Air ConditioningReplies: 19Last Post: 18-10-2010, 02:45 PM -
TEV range & minimum pressure diff issue
By Lc_shi in forum FundamentalsReplies: 2Last Post: 24-04-2006, 04:32 PM -
What's the thermal range of a domestic chest freezer?
By jonno6766 in forum Technical DiscussionsReplies: 7Last Post: 10-01-2006, 10:14 AM -
Automotive A/C Vent Temp Range vs System
By Don Browney in forum Air ConditioningReplies: 1Last Post: 15-05-2002, 06:19 AM