    Flood Back After 2 years..



    Hellow Fellows...

    a 110 cunic meter room @ -30*C for the storage of ice cream.. this room is refrigerated by two systems of a total refrigeration capacity of 6 KW @ Evap. Temp -35*C, the system was running so smoothly from 2 years.. before a week we found one compressor not functioning, we've shift that compressor to our workshop to find it extreamly flooded..!!

    i know fellows that there is too many reasons for flood back, i'll mention those which are not the reason :

    1- Room Loading: the room is for Baskin Robbins Ice Cream, i.e. there is high loading on the room and frequent door opening.. to the matter of low load condition is no there at all..

    2- Suction Accumulator : suction accumulator is there ..

    3- Low ambient : the ambient temp. now is 39*C, i.e. no excessive sub-cooling..

    the question now, how could 1 of the 2 systems got flooded considering that the 2 systems are running on the same conditions !! with a suction accumulator installed too !!!, why didnt the other fail too ?! if there was a problem in the system .. specially with low temp. application .. it was supposed to be rise in the first week of commisioning ..

    i know my posts are all trouble shootings .. i injoy that.. hope there are who share this with me too

    The Best ...


    Too Much Of Something Is Bad Enough

  2. #2
    Join Date
    Sep 2005
    Location
    Australia
    Age
    46
    Posts
    27
    Rep Power
    0

    Re: Flood Back After 2 years..

    2 years is the life time of a low temp system compressor , with out a sump heater. If you dont have one fitted, liquid can mirgrate back to the sump during off cycle, and if you accumulator is undersized you will flood back on start up. Pipework design, can be a problem , and so can the initial gas charge.
    Fit a crank case low temp cut out sensor.
    What type of comp was it?

  3. #3
    Join Date
    Sep 2004
    Location
    Dubai - United Arab Emirates
    Age
    44
    Posts
    37
    Rep Power
    0

    Re: Flood Back After 2 years..

    Dear Mark and Greg..

    Mark, the compressor's pistons cylinder, crankshaft are weared, the piston is even notheched, and the cylinder now is having the upnormal clearence with the piston, moreover the reeds are broken to hundred pieces.. for the oil, the oil is a little bit under it's optimum level, i know there should be no oil, or little oil at least, but i believe it is flood back indications.. what are trying to say Mark.. please advise..

    Greg, actually the contractor did not fit a crankcase heater and i understand this coz it is always hot here ..and the possibilty of flooded start . i dont think so , coz if it was to have flooded start it was to happen in lower ambient throw the 2 years .. the same story for accumulators and initial gas charge ... Greg the type of the compressor is semi-hermetic air cooled..

    The best ..
    Too Much Of Something Is Bad Enough

  4. #4
    Join Date
    Sep 2005
    Location
    Australia
    Age
    46
    Posts
    27
    Rep Power
    0

    Re: Flood Back After 2 years..

    Well reed valves dont smash them selves up. Liquid does that, Liquid in the crank case washes the oil out of the bearing and cylinders so to speak , So you crank case must be getting cold sometime some how.
    a fridgies life is that of never quite understanding.

  5. #5
    Join Date
    Sep 2004
    Location
    Dubai - United Arab Emirates
    Age
    44
    Posts
    37
    Rep Power
    0

    Re: Flood Back After 2 years..

    Dear Greg.. ofcourse it is a flood back, thats what i explained already man, but i mean i doubt it is flooded start.. we've installed hundreds of units without cch, our climate is too hot man ,, besided it is air cooled compressor Greg..
    Too Much Of Something Is Bad Enough

  6. #6
    Join Date
    Sep 2005
    Location
    Australia
    Age
    46
    Posts
    27
    Rep Power
    0

    Re: Flood Back After 2 years..

    Take a suction superheat reading during low load and again at high load, this will answer alot of the questions.
    a fridgies life is that of never quite understanding.

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Flood Back After 2 years..

    HI Mahmoud,

    Have you checked the pumpdown cycle to make sure the unit pumped down? If the liquid line solenoid valve is leaking, the evaporator could have been full of refrigerant on start up.

    Remember, just because one system does something, does not mean all of them have to do it. We saw something similar to this on the last project. Treat each system separately, and look for the common link if there is one. In the last thread the common link was the client.

    Broken valves are usually an indication of liquid slugging. This does not mean the liquid has to be only liquid refrigerant... Oil slugs will do the same thing also.

    However, if the system has been running fine for 2 years, oil logging would have appeared before this time has elapsed.

    Suction accumulators do not prevent floodback if their internal volume is not sufficient. The only way to prevent a floodback on these small systems is to select the accumulator volume so that it holds more refrigerant than the normal system charge. I have seen these selected using the manufacturers tables and still floodback.

    Look forward to seeing how this one turns out.

  8. #8
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Flood Back After 2 years..

    Evaporator completely in ice.
    Fans not running while compressor runs for whatever reason.
    Suction accumulator sized large enough?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #9
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: Flood Back After 2 years..

    Hi Mahmoud,

    How is oil returned to the crankcase?
    I think Marc is probebly on the right track here.
    Does the oil seporator have a heater fitted?
    Does the comp have an oil regulator?
    If so does it work?

    And I would fit a crankcase heater wired into the N/C side of the contactor just in case.

    Chillin
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  10. #10
    Join Date
    Sep 2005
    Location
    Australia
    Age
    46
    Posts
    27
    Rep Power
    0

    Re: Flood Back After 2 years..

    Yeah the defrost fault seems to be high on the list.
    What sort of defrost control do you have.
    a fridgies life is that of never quite understanding.

  11. #11
    slrnick's Avatar
    slrnick Guest

    Re: Flood Back After 2 years..

    Also check if heat exchanger in evap isn't split feeding liquid straight back down suction, bypassing txv

Similar Threads

  1. back pressure valve in chiller
    By vinod in forum Air Conditioning
    Replies: 2
    Last Post: 12-06-2006, 06:29 PM
  2. (Remote) Back bar coolers
    By Chris2005 in forum Commercial
    Replies: 3
    Last Post: 20-03-2005, 08:31 AM
  3. Compressor back pressure rating
    By Cary in forum Fundamentals
    Replies: 9
    Last Post: 05-12-2004, 08:42 AM
  4. Only 52 years and Failing Now
    By johnfarrow in forum Commercial
    Replies: 12
    Last Post: 22-10-2002, 12:42 PM
  5. Low back pressure compressor application
    By Abe in forum Technical Discussions
    Replies: 5
    Last Post: 31-07-2001, 11:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •