    RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?



    Hi,
    I'd like to know your opinions about replacement of R-22 system working (-10 ºC to 36ºC) to R-404-a or Rs 45.
    MY opinion is clear:
    1.-) We know for several years how R-404-a is working, (not the same for Rs 45).
    2.-) Big companies sell R-404-a for several years (not the same for Rs 45)
    3.-) Big manufacturers (Bitzer, Heatcraft, Danfoss... give performance data for their products with R-404-a (not the same for Rs-45).
    4.-) Everybody knows that glide for R-404-a is 0,9, Glide for Rs-45 its said that is 2,8 much bigger than 0,8 recognised by manufacturer...
    5.-) R-404-a price is better than Rs 45
    6.-) BUT, HERE COMES THE PROBLEM:
    You need much extra operations in order to achieve a correct phase out of R22 to R-404-a, than Rs-45.
    So, the offer is finally much expensive with R-404 a than with rs 45.
    So, What to do if my customer is only looking for the cheaper option?
    Thank you for giving me your opinions



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?

    What type of equipment are you looking to change?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jan 2009
    Location
    lleida
    Age
    50
    Posts
    47
    Rep Power
    0

    Re: RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?

    It's a fruit storage center, 4 Bitzer open units 6F.2 of 151 M3/H, with 10 rooms (10 Heatcraft NKT 4x6DB4L EVAPORATORS) and evaporative condenser. water defrost. and 10 danfoss TXV MODEL 55

  4. #4
    Join Date
    Jun 2001
    Location
    Gloucestershire
    Posts
    13
    Rep Power
    0

    Re: RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?

    Why don't you use R422D from DuPont? To use R404A or RS45 you need to ensure pressure rating of system can cope with higher pressures of these refrigerants.

  5. #5
    Join Date
    Dec 2009
    Location
    Spain
    Age
    45
    Posts
    235
    Rep Power
    15

    Re: RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?

    Hi,

    if you recycle that R22, then the operation is not that expensive, as you have until end of 2014 to make a good use of it.

    regards,

    Nando.

  6. #6
    Join Date
    Jan 2009
    Location
    lleida
    Age
    50
    Posts
    47
    Rep Power
    0

    Re: RS 45 (R-434-A) vs r-404-A? For R-22 phaseout?

    Hi ,
    I don't like replacement to R 422 D because of glide 4,5 K i s an important glide (i think), and i don't want to think i f this means a problem in the installation. I prefer to face a problem concerning pressure then glide...
    Hi Fri3Oil System, i agree with you about recycling, but in the two cases it's a "must" isn't it?