    TXV Superheat



    We are all taught the proper TXV superheat settings, but it is important to remember that these are the superheats to be expected when the refrigerated space is at design temperature.

    Unfortunately, when we get there, the space is above design temperature. That's why they called us. We should expect the superheat to be a little higher, but how much higher?

    Maybe Prof Sporlan can help us with this. Is there a chart somewhere or a rule of thumb that we can use to judge whether the superheat setting is somewhere in the ballpark if the space temperature is above design temp?



  2. #2
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Is there a chart somewhere or a rule of thumb that we can use to judge whether the superheat setting is somewhere in the ballpark if the space temperature is above design temp?
    Unfortunately not, or at least not anything like a charging chart for a cap tube or restrictor system. If the TEV is maxed out during pulldown, superheat will effectively be the TD of the evaporator, and it will provide no insight as to the correctness of the valve setting. If the TEV isn't quite maxed out, superheat should fall below the TD of the evaporator, which in theory could provide some insight as to the correctness of the valve setting. Problem here is the TEV is much more difficult to model under these conditions. Unlike a restrictor or cap tube, the TEV has gradient, and it modulates.

    You might be amused to find a short article on the subject of adjusting TEVs in the April 2003 issue of Contracting Business... written by a well known personality within the hvac/r industry.
    Prof Sporlan

  3. #3
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Hmmmm... I was afraid of that.

    I wonder if a procedure could be worked out? Maybe something like reducing the evap airflow to reduce the heat load until the TXV starts modulating?

  4. #4
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    Reducing evap airflow to the point where suction pressures become "normal" for the system would be the way to do it. Should be not problem if one does this well.
    Prof Sporlan

  5. #5
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51
    Can the Prof give a link to the article in Contracting Business for those of us not on that side of the pond?

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    So, for example, if we have a freezer designed for 0F @ 10F TD, we can block off airflow until the SST is -10F to check and perhaps even adjust TXV superheat.

    Sounds like a winner.

  7. #7
    Join Date
    Jan 2002
    Location
    Austin, Texas
    Posts
    716
    Rep Power
    23
    A very insightful thread..... thank you.

  8. #8
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    It would, of course, help if the airflow was reduced evenly across the face of the evaporator, which could be done reasonably well with fan speed control. Using cardboard may give less than ideal results, however....

    The Prof could not find a link to his article, however.
    Prof Sporlan

  9. #9
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    It would, of course, help if the airflow was reduced evenly across the face of the evaporator, which could be done reasonably well with fan speed control. Using cardboard may give less than ideal results, however....
    On unit coolers, obstructing the discharge air evenly is probably best when a fan speed control is not available. The higher static pressure on the outlet of the evaporator will provide a more even flow across the evaporator, than just letting portions of the evaporator see differences in flow across different circuits.

    I think what the professor worries about is that a distributor circuit could deliver the wrong message to the TEV if the air flow favors or disfavors a circuit when airflow is not evenly distributed.

    My guess is that this consideration becomes less important when you are lowering airflow by constricting ducted air such as in the air returns of display cases and air conditioners.

  10. #10
    Join Date
    Mar 2001
    Location
    St. Louis, MO
    Posts
    509
    Rep Power
    24
    I think what the professor worries about is that a distributor circuit could deliver the wrong message to the TEV if the air flow favors or disfavors a circuit when airflow is not evenly distributed.
    Bingo!
    Prof Sporlan

  11. #11
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    Since circuits are horizontal, the entering air could be blocked so long as we block vertically (top to bottom), and avoid blocking horizontally.

  12. #12
    Join Date
    Feb 2001
    Location
    Tampa Florida
    Posts
    1,076
    Rep Power
    25
    Since circuits are horizontal, the entering air could be blocked so long as we block vertically (top to bottom), and avoid blocking horizontally.
    I can't come up with a good argument for your suggestion, other than why bother. Blocking the discharge changes nothing about the entry of the air over the coil (I am assuming we are talking about a unit cooler).

    Blocking the return air changes not only the air flow velocity across the evaporator, but also, where the air crosses the evaporator. To me, it invites unnecessary confusion. And because we are changing things we have to consider all sorts of possible nuances.

    I have seen some different circuitings of unit cooler coils. I am not sure all circuits are always balanced... I see return bends skipping a row, I have seen tripod return bends, where flow from two circuits become a single circuit, etc.

    But I have to ask why? You can use the same piece of cardboard on the opposite side of the coil and achieve a guaranteed balanced reduced air flow across the evaporator.

    A vertically restricted intake air flow may induce more air past a leaky tubesheet that influences TEV operation.

    I think best practice is to restrict discharge air flow. It changes little about how the air will flow over the evaporator . Restricting intake airflow changes a lot of things regarding evaporator behavior.

    I have no good argument, but if I have a piece of cardboard, I think the smart thing to do with it is put it on the air-discharge side of a unit cooler.

    I think maybe that blocking any flow should be done from the discharge and not from the return... air conditioning, supermaket cases, condensers.

    Messing around with the air that is entering a heat exchanger should preserve an equal air flow through the heat exchanger. I think the best way to do it is not by blocking the air or fluid entering the heat exchanger, but by blocking the air or fluid that is exiting the heat exchanger.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35
    There are various ways to do this, and some will be better for some circumstances than others. It's all good.

  14. #14
    Join Date
    Nov 2007
    Location
    Romania
    Age
    58
    Posts
    14
    Rep Power
    0

    Re:Books

    Good Day Mrs. Gary

    My name is Suta Eugen and i am from Romania ,sory my english is not so good .

    I am interested too bay your books if is a posibility too pay at delivery + delivery taxes of cours.

    I am traing too contact you by e- mail but is not possiblle ,my e-mail is *********** if you are so kaind too send to my a e-maill whit your opinien.

    Thank You
    Last edited by frank; 16-11-2007 at 08:14 PM. Reason: Please do not post e-mail addresses in the open forum

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: TXV Superheat

    My books are available at:

    https://www.merchantamerica.com/tmethod/

  16. #16
    Hokiewolf's Avatar
    Hokiewolf Guest

    Re: TXV Superheat

    This is an old thread, but I was researching TXVs and superheat and found the article you referenced. It really helped out a co-worker working a job that had confounded several others over the past week. Thought others might enjoy your article here:
    http://contractingbusiness.com/residential/cb_imp_5549/
    The error chart from Brainerd compressor is on page 14 here:
    http://www.brainerdcompressor.com/_p...d%20Manual.pdf

Similar Threads

  1. Carrier 23xl chiller-Low discharge superheat alarms
    By Bradysmill in forum Trouble Shooting
    Replies: 7
    Last Post: 25-04-2010, 07:43 PM
  2. TEV superheat setting and low temperatures
    By DaBit in forum Fundamentals
    Replies: 11
    Last Post: 01-03-2010, 02:11 AM
  3. Superheat debate
    By zolar1 in forum Technical Discussions
    Replies: 5
    Last Post: 08-02-2008, 09:57 PM
  4. Superheat
    By shogun7 in forum Fundamentals
    Replies: 24
    Last Post: 23-08-2004, 05:54 PM
  5. Setting superheat settings
    By Abe in forum Commercial
    Replies: 12
    Last Post: 10-06-2004, 02:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •