Results 1 to 5 of 5
  1. #1
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Bock Compressors



    Hi I have a little complication about Bock compressors
    I calculate capacity and I chose
    Bock HG6/1410-4 but there is also HG6/1410-4 S
    What is the differents between two model ( What is he S mean ? )

    S have little more cooling capacity.



  2. #2
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Bock Compressors

    R-22 APPLICATION

    1) HG6/1410-4S ............... MOTOR CAPACITY 30 KW ........ MAX EVAPORATING TEMP : 12.5 deg C
    2) HG6/1410-4 ................. MOTOR CAPACITY 26 KW ........ mAX EVAPORATING TEMP : ( -5 ) deg C

    S means stronger motor ...............

  3. #3
    Join Date
    Oct 2009
    Location
    turkey
    Age
    40
    Posts
    45
    Rep Power
    0

    Re: Bock Compressors

    Thanks koranne
    I use 404A and evap is -5
    You said Max evap is -5 but Whan I chose the evap -10C in Bock select tool there is not error ?

  4. #4
    Join Date
    Mar 2009
    Location
    uk
    Age
    61
    Posts
    5
    Rep Power
    0

    Re: Bock Compressors

    The S means rated for higher evaporating temperatures - look at application charts on Bock website.

  5. #5
    Join Date
    May 2006
    Location
    India
    Age
    74
    Posts
    399
    Rep Power
    18

    Re: Bock Compressors

    I CITED R-22 AS AN EXAMPLE ........... R-404A WILL HAVE HIGHER CONDENSING PRESSURE & LOWER DISCHARGE END TEMP ..........HENCE REFRIGERANT PLAYS PART IN THE FORMATION OF COMPRESSOR SAFE ENVELOPE .

    IF ANY DIFFICULTY GET IN TOUCH WITH ME ON MY PM : ddk0123@gmail.com