    Question how do i know my system is charged well



    hi all I知 not sure if my question is typical are strange in this great forum I致e a black point in my life it's the amount of pressure at the suction side .I知 dealing with kitchen freezers and refrigerators and even a domestic refrigerators they are working with R-22 ,404a ,R-12, 134 if we suppose all the system components working properly and I知 talking about forced air cooling system (a fan mounted in the front of evaporators )what is the readings should I get on the suction side help me by explaining or tell me if there is any site I can get these information from or any documents that help me to learn thanks all



  2. #2
    Join Date
    Sep 2005
    Location
    TUNISIA
    Posts
    10
    Rep Power
    0

    Re: how do i know my system is charged well

    thanks botrous you are talking about the volume of refrigerant but i saw many of them using the guages and only the low pressure guage and feeding the refrigerant until the guage readings reaches to 1.5 for R-22 bar or 1 bar R-12 i've never seen a frigorist uses the volume quantity as a reference

  3. #3
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: how do i know my system is charged well

    If you want to use the gauges to determine if the refrigerant is enough in the system , you need to know many parameters , i've sent you a link via email that explains that .
    But doing that and wait the gauges to mark 1 or 1.5 bar , i donno , it doesn't seem to me to be a scientific and adequate method.

    Regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  4. #4
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: how do i know my system is charged well

    OOPs maybe someone else is interrested and wants the file , here is a link for the file . . . just click on the download

    http://www.sporlan.com/10-135.htm

    Regards
    Last edited by botrous; 24-09-2005 at 10:42 PM.
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: how do i know my system is charged well

    Quote Originally Posted by botrous
    Yes, the good old Sporlan site, a vast source of interesting knowledge A timely reminder Botrous, thanks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: how do i know my system is charged well

    Yes, the good old Sporlan site, a vast source of interesting knowledge A timely reminder Botrous, thanks
    Always welcome
    A friend reminded me of the sporlan site 2 days ago . . . . so i had a timely reminder to

    Regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  7. #7
    Join Date
    May 2005
    Location
    Australia
    Age
    83
    Posts
    63
    Rep Power
    19

    Re: how do i know my system is charged well

    Botorous with sunnys on....in disguise, hiding from the cops or out to impress the ladies...lol
    100% is possible 100% of the time

  8. #8
    Join Date
    Aug 2005
    Location
    iraq
    Age
    67
    Posts
    130
    Rep Power
    19

    Re: how do i know my system is charged well

    Quote Originally Posted by duraid
    hi all I知 not sure if my question is typical are strange in this great forum I致e a black point in my life it's the amount of pressure at the suction side .I知 dealing with kitchen freezers and refrigerators and even a domestic refrigerators they are working with R-22 ,404a ,R-12, 134 if we suppose all the system components working properly and I知 talking about forced air cooling system (a fan mounted in the front of evaporators )what is the readings should I get on the suction side help me by explaining or tell me if there is any site I can get these information from or any documents that help me to learn thanks all
    hi dear
    the scientific way to determine the frion charge in a system is the sight-glass,when the bubbels disappears ,means the system is fully charged
    the pressure gauge give you a range of pressur cause the ambiant temperature affect the refrigerent charge
    for the domistic refrigerators,the weight of refrigernt (writen on name plate)is your choice of charging
    all regards

  9. #9
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: how do i know my system is charged well

    What if there isn't a nameplate?
    What about superheat?
    Filling a sightglass till bubbles are gone isn't a scientific way to determine correct filling?
    What about subcool, flashgas when filling till sight glass is full?

    This was covered already in the past and Chemi gave as far as I remember a solution which most of us are using to fill almost any domestic system.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  10. #10
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: how do i know my system is charged well

    Quote Originally Posted by Peter_1

    This was covered already in the past and Chemi gave as far as I remember a solution which most of us are using to fill almost any domestic system.
    G'day Peter

    What was the method?
    Which thread was it on.?
    I would be interested to read.

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: how do i know my system is charged well

    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: how do i know my system is charged well

    Its Simple

    You charge until the frost line appears just after the end of evap coil.

    Then you have full charge

    This applies small domestic systems, cap tube

  13. #13
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: how do i know my system is charged well

    Botorous with sunnys on....in disguise, hiding from the cops or out to impress the ladies...lol
    Both , disguising from the cops and impressing the ladies
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  14. #14
    Join Date
    Sep 2005
    Location
    TUNISIA
    Posts
    10
    Rep Power
    0

    Re: how do i know my system is charged well

    thank u guys very much all of you .i received the link you sent potrous it's very useful and i'm still reading it i know that the use of guages only is not a scientific even all the system components are okay because variation of ambient temp.thanks a lot and i'll keep in touch

  15. #15
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: how do i know my system is charged well

    potrous
    It's Botrous , for who , who find it difficult to spell , try to call me pierre my real name , maybe i get it written right

    Welcome Duraid , keep on visiting the forum , it's a great place to learn and to share your knowldge

    Regards
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  16. #16
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: how do i know my system is charged well

    Quote Originally Posted by Aiyub
    Its Simple

    You charge until the frost line appears just after the end of evap coil.

    Then you have full charge

    This applies small domestic systems, cap tube
    Hello Aiyub.
    This was the method I was taught as an apprentice.

    One engineer I know stops the evaporator fan and uses the same method.

    He claims that the cabinet doesnt have to be at temperature to do it this way.

    Anyone heard of this?

  17. #17
    Join Date
    Dec 2004
    Location
    Australia
    Age
    52
    Posts
    519
    Rep Power
    20

    Re: how do i know my system is charged well

    Quote Originally Posted by Peter_1
    Thanks Peter.

  18. #18
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: how do i know my system is charged well

    One engineer I know stops the evaporator fan and uses the same method.
    If im working on a cap system and im not weighing the gas in I always use this method, I thought everybody did this?
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  19. #19
    Join Date
    Sep 2005
    Location
    Australia
    Age
    68
    Posts
    7
    Rep Power
    0

    Re: how do i know my system is charged well

    A sight glass is only an indication of moisture in the system..that is why they are called moisture indicators..a sight glass installed in a horizontal plane will not be a correct indication of refrigerant charge..to be effective for that purpose they need to be installed in a vertical plane..and..do not forget that if you have a drier/strainer in the system prior to the sight glass and there is any form of restriction in the drier/strainer then the sight glass will bubble..great way to overcharge the system by using the clear sight glass method.

  20. #20
    Join Date
    Nov 2003
    Location
    North Wales
    Age
    48
    Posts
    74
    Rep Power
    21

    Re: how do i know my system is charged well

    Hi all
    No offence but I haven't come across many domestic refrigeration systems that use a sight glass.

    Is R12 still legal to use in Tunisia.

    Also I agree with the method where you stop the evap fan and charge by the iceline.
    It works evey time.

    Neil
    If you can't see it, it can't hurt you.

Similar Threads

  1. Daikin fault codes
    By Chris2005 in forum Air Conditioning
    Replies: 45
    Last Post: 21-03-2012, 10:09 PM
  2. System Burn Out Troubleshooting
    By altaf22m in forum Technical Discussions
    Replies: 13
    Last Post: 07-05-2010, 09:24 AM
  3. Replies: 19
    Last Post: 15-04-2008, 07:03 PM
  4. Refrigeration system proposal; comments please.
    By DaBit in forum Technical Speculations
    Replies: 13
    Last Post: 01-01-2003, 03:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •